heat control

heat control

heat control

(OP)
Hi.

I like to control an electrical underfloor heating termostat with my PLC (Beckhoff). I like to be able to set setpoint (Temperature) and read flor temperature in the PLC

4-20ma or 0-10V is good, but also any bus signal is fine

However I cant find a sutible termostat for this job. Any suggestion to how this can be done? Dont want to use KNX devices.

Thanks

RE: heat control

(OP)
KNX or EIB is a bus system. It is often used in building automation on light and heat control. The components are very expensive but they have good functionality. So I try to find a way of controlling the heat without KNX devices.  

RE: heat control

Thanks for the lesson.

Umm You question is still not a 100% though.  You say you want to control the heat with a PLC but then you say you can't find a thermostat.  A thermostat is  a temperature controller.

Unless you are talking about a wall box that measures the temperature and provides an adjustment readable by a PLC?


If this is what you're referring to I have not seen anything like it.   I will say I have found wall mount housings that look like traditional thermostats.  They have little grates in them so the air will pass thru them.

You could get a pot of a value that your PLC can read and use it as a voltage divider that will provide the "setting".  Then add whatever temp sensor your PLC can use.  RTD, or TC, or ??   Essentially roll your own.

Keith Cress
kcress - http://www.flaminsystems.com

RE: heat control

(OP)
Ok.

I cant drive big loads from a PLC, so I need a power controller. The PLC is used as a main controller in a distributed control system in house automation. So I found a way of doing this using PLC with I/O's,  temperatur sensor and a SCR power controller. Controlling the temperature by a PID block in PLC. The heat element is connected to the SCR:)

Now I can set temperature setpoint or load in %/max load.



 

RE: heat control

Your best bet would be to control the temperature with  PLC using a Thermocouple input whether this is a single input or a multi.
This brings in the resistance to a card that the PLC can read you do the logic to output a 4-20Ma output to your SCR then using a PID in the PLC  you can attain great temperature control.

There is a better solution and that is a temperature controller, West/Partlow makes a T/C input with a 4-20 output, Cheap, easy to program and it has the algorythm for the PID.
I would however use an RTD instead of a thermocouple same readings but you can take an RTD longer distances without having an effect on the reading.

RE: heat control

(OP)
Thanks for good suggestions.

I will go for PLC, Thermocuple, PID, and SCR. I'm using Beckhoff PLC. They have a autotuning PID for temperature control. I want to control temperature from the PLC as it is a part of a bigger building automation system and there is sentralized functions and readings as well.



 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources