how to calculate the seismic load of CMU screen wall

how to calculate the seismic load of CMU screen wall

how to calculate the seismic load of CMU screen wall

(OP)
I have a 12" CMU wall (solid grouted) with 13.3' high. it is a screen wall. the verical reinforcement is #6 @ 18" OC

 I have calcualted the SDs=0.61, SD1=0.58 (design spectral response).  

How to calculate lateral seismic load?

Thanks

RE: how to calculate the seismic load of CMU screen wall

Are you sure of the reinforcing?  Usually CMU reinforcing is on an 8" module.  I would expect 16" on center.

Just use the pertinent IBC equations for the lateral seismic forces.

Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask

RE: how to calculate the seismic load of CMU screen wall

Agree with Mike on the spacing-See ASCE 13.3

RE: how to calculate the seismic load of CMU screen wall

See 12.11.1 of ASCE 7-05.  Apply force indicated as a lateral force at center of wall mass (0.4SdsI).   

RE: how to calculate the seismic load of CMU screen wall

(OP)
yes. it is 16" OC.

in the formula 0.4SDsI, is that I can be same as the adjacent building.

Thanks.

RE: how to calculate the seismic load of CMU screen wall

When I do seismic calcs on a cantilevered fire wall or screen wall, I break the wall into 4 quadrants of height and run the numbers as a 4 story building. I beleive this is conservative but it helps in the p-delta calc and the top heavy nature of a tall cantilevered wall.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources