Concrete Edge Load / Direct Shear
I was asked to review another's design for attachment to an existing concrete curb.  The 5000# load is for direct suspension of personnel.  See sketch.
My initial response was that you wouldn't want to load a curb that close to a free edge in this fashion.  The designer wants this backed up by calcs.  His calcs use ACI  11.12 two-way shear, using d = 4". (see the longer, downward crack)
I argued that it couldn't be considered reinforced, which I believe is obvious, and that a failure could likely look like the upper, shorter crack in the sketch.
Thoughts?  Furthermore, how would you back it up with calcs?
RE: Concrete Edge Load / Direct Shear
Why don't you put a steel bearing plate under the nut of sufficient size so that the smaller crack does not happen, and the developed shear cone is larger?
I do agree that the section is not properly reinforced for shear currently.
With regard to the calcs, I would just use root f'c times the most likely cone surface area to develop for the available resisting shear force.
Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask
You also can't show by ACI that the curb won't fail in direct shear at its interface with the floor.  The vertical #4 bars must be fully developed into the curb (i.e. hook or full development length) to create the necessary shear friction between curb and floor.