I am troubleshooting an intermittent generator problem. Information from customer is generator shuts down after running approx 6 hours. Only alarm is under voltage. Not sure if this is a secondary alarm coming in after an engine problem occurs.
I am looking for a multi channel recorder to monitor generator voltage, freq, governor actuator, pmg, etc.
I need approx 500ms update max ... quicker would be nice.
I would like it to connect to a computer and retain approx 30 minutes of information.
Does such a device exist?
Thanks
BB
I am looking for a multi channel recorder to monitor generator voltage, freq, governor actuator, pmg, etc.
I need approx 500ms update max ... quicker would be nice.
I would like it to connect to a computer and retain approx 30 minutes of information.
Does such a device exist?
Thanks
BB





RE: Test Equipment Needed
Muthu
www.edison.co.in
RE: Test Equipment Needed
Just looking for a good recorder to give me a real time sequence of events.
BB
RE: Test Equipment Needed
Developed to locate 'non-existing and mysterious' faults, intemittent faults or plain long term supervision with high time resolution. Extended zoom and reference curve overlay. Export data to Excel if needed.
We love it. We wanted it for thirty years and now we have it. We named it Arcus with a blink at ABB Argus.
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: Test Equipment Needed
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Test Equipment Needed
http://w
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: Test Equipment Needed
Muthu
www.edison.co.in
RE: Test Equipment Needed
http://www.electrorent.com/
RE: Test Equipment Needed
Thanks again
BB
RE: Test Equipment Needed
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: Test Equipment Needed
Depending on the place, do not discount mischief!
Aimlessly gathering slew of information could be just waste of time and money. How about having a couple of experienced people watch it, say after 5 hrs. Depending on how sophisticated the engine controller and display are, it can inform a lot.
Also there is much to the story that is not told. What do you have to do to bring the machine back online?
Rafiq Bulsara
http://www.srengineersct.com
RE: Test Equipment Needed
I am not sure if it is breaker tripping on under voltage and generator continues running, or if generator is shutting off. As designed, 27 should trip breaker only.
Just wanted right test equipment to catch the event when it happens as it is such a long time between events.