66kV Riser Pole Arrestors

66kV Riser Pole Arrestors

66kV Riser Pole Arrestors

(OP)
We are converting a 1200m section of overhead 66kV to underground (3 x 1C 630mm² CU XLPE). Looking for suitable 66kV Riser Pole polymer arrestors to install at both pole top ends. Can anybody help.

RE: 66kV Riser Pole Arrestors

These are very common products. Is there something unusual about your situation?

Try Cooper, Hubbell or ABB.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: 66kV Riser Pole Arrestors

I don't know that riser pole arresters are available at that high a voltage.  They are normally for distribution.  I think an intermediate class or station class arrester would be suitable (these are ANSI classifications).

RE: 66kV Riser Pole Arrestors

Good point. "Riser pole" style quit at 36kV. I guess I was thinking station type being mounted on the riser pole.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: 66kV Riser Pole Arrestors

You could make special crossarms for your riser pole so you could install station mount arrestors.

RE: 66kV Riser Pole Arrestors


Pacific Gas & Electric in some places has used station-class arresters on riser poles in areas of very-high lightning incidence.  My understanding is that the brackets they use in this application are made by Aluma-Form.
  
 

RE: 66kV Riser Pole Arrestors

(OP)
Thanks for all the feedback todate.
Thoughts so far:
With nominal Line to Line Voltage of 66.0kV rms.
Typical Max line to Line Voltage of 72kV rms.
Max Line to Ground Voltage 41.6kV rms (On 3 phase systems the line to ground voltage is divided by 1.73).
We have determined how high the line to ground voltage of the unfaulted phases will rise to during a ground fault.
We have also calculated Potential System Over voltages.

Since Riser Pole Arrestors quit at 36kV we are looking at installing 72kV Intermediate class arrestors with an MCOV of 57.0.
Comments would be apprieciated.  

RE: 66kV Riser Pole Arrestors

What's your calculated maximum line-to-ground voltage?

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: 66kV Riser Pole Arrestors

(OP)
Max Line to Ground Voltage as stated above

RE: 66kV Riser Pole Arrestors

You could probably use 60/48kV.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: 66kV Riser Pole Arrestors

MCOV=42 kV unless the TOV is insufficient.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources