Grounded Y û Y MV transformers compare to ? û Y gounded Tr

Grounded Y û Y MV transformers compare to ? û Y gounded Tr

Grounded Y û Y MV transformers compare to ? û Y gounded Tr

(OP)
Would any body tell me what are the benefits of both grounded Y – Y medium voltage transformers compare to generally used Δ – Y grounded transformer?  

RE: Grounded Y û Y MV transformers compare to ? û Y gounded Tr

Less chance of ferro-resonance.

Grounded wye winding can have graded insulation and insulated for line-ground voltage which may make it less expensive.

 

David Castor
www.cvoes.com

RE: Grounded Y û Y MV transformers compare to ? û Y gounded Tr

The grounded wye-grounded wye provides a zero sequence connection between primary and secondary while the delta-grounded wye does not.  The delta-grounded wye provides a ground source on the wye side while the grounded wye-grounded wye does not (presence of a delta tertiary changes things).  For some applications one set of characteristics is more desirable than the other.

RE: Grounded Y û Y MV transformers compare to ? û Y gounded Tr

(OP)
Hi Dpc, and David, thank you very mach for your response. Now I believe that in my case where the voltage levels are 13.8 KV and 4.16 KV with transformers power at 5 MVA levels, DRY types the transformer dimension would be the ONLY ADVANTAGE for Y – Y transformers selection.

RE: Grounded Y û Y MV transformers compare to ? û Y gounded Tr

Hi.
Is depend on your application.
What is a 13.8kV grid.
You have check, if you can use ground wye, it will be second ground point in the sistem, not always possible.
Best Regards.
Slava

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources