cantilever hollowcore design
I am designing a Hollowcore slab cantilever 7 foot out. I need to check both service and strength. I think I should design the bending strength of the section at cantilever for 1.2D+1.6L+1.0(P*e) with mild steel on top. the hollow core provider think for strength design we don't need to add the P*e which is considered internal force.
I didn't find anywhere in the code back up my thought. Does anyone have thoughts/experience on this.
Thanks a lot
Thanks a lot
RE: cantilever hollowcore design
BA
It should be included in the calculations of the section capacity. It will possibly reduce capacity depending on the depth to the PT strand relative to the neutral axis and centroid of the compression force.
PS I still cannot believe that anyone will sign off on a design based on load tables from a suppliers literature!
BA
Anytime you vary from the standard products, you raise the cost and delay the production and delivery. If you are convinced you need to vary from the locally available products they can be be obtained and cost premium and delivery time could be reduced if it is a large project.
I would suggest you contact the largest local supplier (who probably has more products and engineering)to determine available options and costs. Then you can design and specify what you choose and let the suppliers fight for the job. Specifying and CPI certified plant is a help, but most (80%+) good suppliers are certified and maintain great records for the future.
Dick
Engineer and international traveler interested in construction techniques, problems and proper design.
I agree with you that we shouldn't blindly follow manufacturers load tables; but do you go through hand calculations when specifying Hilti anchors? Do you test assemblies when specifying Simpson hangers?
It is in the manufacturers best interest to provide accurate, reliable information to the specifying professional. It is up to us to interpret their published capacities correctly.
I am not quite clear on why the negative moment at the support resulting from the bottom strands should not be added to the applied moment when designing top steel.
BA
Thanks for the in put. I just couldn't get my mind strait on this issue. If the concrete cracked and only 2" for stress block in compression, the PT force still will increase the concrete compressive stress in the stress block.
This could:
1. reduce the capacity of the section
2. Might cause structural failure model with concrete crushing which is not a ductile failure we desired for concrete design.
I think we still need to consider the PT force for ultimate strength design.
I agree that the PT force will increase the stress in the compression block. The second page of dik's reference says that when the bottom prestress is very heavy, a strain compatibility analysis should be performed.
For the example in that article and probably for most practical situations involving hollow-core slabs, the depth of the compression block would not change enough to significantly alter the moment resistance of the section. But, you are correct...it should be considered.
BA
The danger I would foresee in debonding strands in a long prestressing bed is that you debond the wrong portion of the strand, but there is no question that debonding would work. What do you use to debond the strand, a plastic sheath?
BA
It is still an internal action. Its effecvt on ythe moments in the section will come out i n the capacity side of the calculation if the calculations are done properly by strain compatibility. As suggested above, it will cause a deeper neutral axis due to the compression. Also, As the tendon is below the neutral axis, its effect on the section capacity will be to reduce the capacity.
RE the comment about Hilti anchors. yes I will believe test data for something whos capacity can only be determined by test. That is also why I accept the shear capacity logic in concrete members.
But for things I can calculate based on accepted principles, I will calculate it and not accept some salesman's capacity charts!
I agree that the compression caused by the lower tendons will reduce the moment capacity of the section because the depth of compression block will increase, resulting in a slight reduction in moment arm. However, in normal situations, the reduction would be so small as to be almost negligible.
But, by all means, if you are concerned about it, calculate the effect and place a little more top steel in the slab to compensate for the slight reduction in moment arm.
To summarize, you need to provide enough top steel to resist a factored load of 1.2*D + 1.6*L (in Canada it would be 1.25*D + 1.5*L), taking into account the additional compressive stress in the lower fibers of the slab resulting from the bottom prestressing.
BA
Dik
The prestressing force in the cantilever is an internal force and is not included in the factored loads.
Slabs are designed by manufacturers acting as simply supported members with bottom tendons. So they have cetificates for such action. However manufacturers allow for cantilevers but their length are limited (from my experirnce up to 1500 mm circa). It is just calculated as single reinforced beam section.
The reason of limited cantilevered length are:
1. Hollow core slabs have precamber so your unloaded cantilever will have some deflection at start. Hollow core manufacturers are not very willing to give value of this deflection as it can varry and they do not know this exact value.
2. To achieve cantilevered action of plank some end cores need to be opened gently and filled with structural concrete.
Usually only every second core or every third core is opened and filled with concrete. For short cantilevers is easy to assume some bar lengths to get correct anchorage.
For longer cantilevers you need to provide this length and manufacturers need to take it into account. And they are not very happy when more than half of slab need to have filled cores. Also they can not give you warranty that bars will be cast in core with min top cover so usually cover is assumed much more greater.
In your case: about 2.1 m cantilever I would talk to precast planks manufacturer at begining of projrct design
kris
Thanks for your input. the manufacturer's opioning was disregard the internal PT force for strength design. With everyone's input here I think we are clear a strain compatibility analysis is required with the PT stress considered.