Is there a way around High GPR

Is there a way around High GPR

Is there a way around High GPR

(OP)
Claculation shows that GPR is 11000V , very high fault current which is around 28000A.
Step and touch potentials are fine and within limits. would this cause a serious damage to the equipments?

RE: Is there a way around High GPR

The GPR can cause problems if you have any cables entering the facility that are grounded remotely, like telephone cables.
 

RE: Is there a way around High GPR

(OP)
Is that the only concern?
What if we use fiber optics for communications?
 

RE: Is there a way around High GPR

(OP)
I also think when distribution line neutral wire or transmission line sky wire are connected to grid, high GPR would increase the voltage on those lines as well and all insulating equipments on Neutral line will be exposed to this high voltage.

RE: Is there a way around High GPR

Also, you can have high transferred potential to equipment that is connected to the facility ground.  See IEEE std 80 and http://www.groundperfect.com/transfer.htm
 

RE: Is there a way around High GPR

Maybe some additional info here:  

http://www.positronpower.com/en/

The telco will be concerned about GPR as a safety issue.  

Use of fiber for data and phone lines can certainly reduce some of the concerns.   

David Castor
www.cvoes.com

RE: Is there a way around High GPR

(OP)
I just looked up some info and inspection authorities are asking for " Zone of Influence" !!!
any idea how this can be calculated?

RE: Is there a way around High GPR

This is the area where the earth surface voltage is greater than a particular value, usually 300 volts.  Earth surface voltage decreases with distance away from the grounding system.  I have calculated the zone of influence using grounding analysis software and making a contour plot of earth surface voltage, with 300 volts as one contour.

If you have a GPR of 11,000 volts, your zone of influence probably covers the whole county.winky smile

Are you sure that you are accounting for ground fault return current flowing in neutrals or shield wires instead of through the earth?  If your grid resistance is 0.4 ohms and half of the fault current returns to the source through a metallic neutral conductor, then the GPR is only (1-0.5)·28000·0.4 = 5,600 volts.
 

RE: Is there a way around High GPR

(OP)
There are two distribution line coming to the sub and the software calculates the overall impedance. I assumed a typical value of 100 ohm for tower footing resistance-to-ground and this didn't affect the overall impedance too much.It just brought it down from 0.4 to 0.37.
"
Are you sure that you are accounting for ground fault return current flowing in neutrals or shield wires instead of through the earth?  If your grid resistance is 0.4 ohms and half of the fault current returns to the source through a metallic neutral conductor, then the GPR is only (1-0.5)·28000·0.4 = 5,600 volts."

CYMGRD doesnt give me the option of choosing how the return current goes back to source!!
 

RE: Is there a way around High GPR

CYMGRD will not calculate the current split factor?  You can use the tables in IEEE-80-2000 to estimate the split factor based on some assumptions.

This will lower you GPR as jghrist has described, but each site is different and should be calculated.

RE: Is there a way around High GPR

If CYMGRD calculates the overall impedance to remote earth (two neutrals and earth path in parallel), then you would use the total ground fault current to calculate GPR.  This isn't the way IEEE Std 80 calculates GPR.  I'd be curious to find out what method CYMGRD uses to calculate the overall impedance.  What is the resistance of the ground grid by itself?

According to the CYMGRD brochure, it computes Rg and

Quote:

Current Split Factor (SF) estimated from substation configuration data as per IEEE Std. 80-2000.

RE: Is there a way around High GPR

See IEEE Std 367 for guidance on determination of ZOI.

 

David Castor
www.cvoes.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources