I have an AC motor of about 1.5HP, run with 240V AC single phase. The motor is about 300 ft from the controller, which switches only one leg of the 240V. At the motor, then, I have a ground wire, one leg always hot, and one switched line. Typically on/off abut 60/40% on a 5-minute total cycle.
I'd like to fabricate a "fail to run" counter. Increments a counter if after oh 15 seconds of power applied, the motor is not drawing the expected amperage. Maybe there's a better way to do this.
I have a current sensor time delay cube relay and another time delay relay - to ignore the startup and shutdown portions of the cycle. And a totalizer that takes any voltage [in this scenario] or a contact closing. Easy enough.
BUT... the TD relays/ current sensor work on 120V AC, not 240. At the motor, I have two "120V" wires... but no N wire to serves as the other line. I understand using the ground wire, though it would work, is not to be done.
It'd be a major expense to have a N wire brought from the panel. What about tapping a fairly nearby lighting or similar circuit for an N wire? The only other option seems to be go shopping for 240V versions of the TD Relay/ Current Sensor. Was hoping to avoid a huge outlay of $ in these tight times, since I have the components... they just require a different power supply.
Suggestions for bringing in an N wire, or an alternate method to count Fails To Start [PLC?] ???
Thanks!
I'd like to fabricate a "fail to run" counter. Increments a counter if after oh 15 seconds of power applied, the motor is not drawing the expected amperage. Maybe there's a better way to do this.
I have a current sensor time delay cube relay and another time delay relay - to ignore the startup and shutdown portions of the cycle. And a totalizer that takes any voltage [in this scenario] or a contact closing. Easy enough.
BUT... the TD relays/ current sensor work on 120V AC, not 240. At the motor, I have two "120V" wires... but no N wire to serves as the other line. I understand using the ground wire, though it would work, is not to be done.
It'd be a major expense to have a N wire brought from the panel. What about tapping a fairly nearby lighting or similar circuit for an N wire? The only other option seems to be go shopping for 240V versions of the TD Relay/ Current Sensor. Was hoping to avoid a huge outlay of $ in these tight times, since I have the components... they just require a different power supply.
Suggestions for bringing in an N wire, or an alternate method to count Fails To Start [PLC?] ???
Thanks!





RE: 240V AC Motor Fail to Start counter/ 120V lacks N wire
Or were you planning on using this as part of your protection scheme?
------------------------------------------------------------------------
If it is broken, fix it. If it isn't broken, I'll soon fix that.
RE: 240V AC Motor Fail to Start counter/ 120V lacks N wire
Simplest solution using what you already have, just add a small 240-120V Control Power Transformer to give you 120V in this box.
I would rather just find a current monitor that has a built-in time delay and runs on 240V, they are out there.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: 240V AC Motor Fail to Start counter/ 120V lacks N wire
A book full of all kinds of malpractice and general tricks for using 3-phase motors where there is only single phase, using 120V motors on 240V supplies, and things of that ilk is called Electric Motors written by Jim Cox. It's intended for the home workshop user, not the professional engineer, and some of the things he describes might be ok in a home workshop but couldn't be used in a commercial product. Might be worth spending a few pounds / dollars / etc on a copy from Amazon.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: 240V AC Motor Fail to Start counter/ 120V lacks N wire
Note: Motors for use on 120:240V supplies are rated 115:230V