current phase imbalance

current phase imbalance

current phase imbalance

(OP)
my client recently had a utility company phase loss.
After correction, I checked the phases for current.
A phase 1077A, B phase 1116A, C phase 354A
The transformer is a 750kVa 277/480v secondary.
 

RE: current phase imbalance

Apart from "That's nice!", what do you expect us to say?

There's clearly a lot of single phase load either connected between A-B, or A-N and B-N, or a combination of both. You could re-distribute the loads to improve balance, but is it actually causing a problem to warrant the effort?
   

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: current phase imbalance

(OP)
There are no single phase loads to speak of.

RE: current phase imbalance

Then there is a problem with one of the major loads. I don't feel very smart when saying that.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: current phase imbalance

Not to mention the phase A and B are overloaded. 750 kVA transformer's rated full load current at 480V is 900A. Keep an eye on the transformer for smoke!

Are there 480V single phase loads?

I would also double check the amp readings and check the method, meter, CTs or anything else that is used for the measurements.

Rafiq Bulsara
http://www.srengineersct.com

RE: current phase imbalance

Was this a problem before the utility phase loss?  Where are you getting the readings?  If it is a panel meter, then it may have a problem and I would use a clip on to see if the amps match what the meter indicates.  Ask the utility to see what their meter shows as well.

Rafig is correct about the loading.  Somehow I feel you need to do some more checking and would love to hear the rest of the story once you get more info.

Alan

RE: current phase imbalance

I would also be verifying the currents with another meter.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: current phase imbalance

(OP)
I rechecked the loads yesterday and they were normal,
A 738A   B 723A   C 696A.
I had the utility company set up ma five day monitor to see what is going on. I checked all larger motors and loads were normal.
Interesting! Any thoughts?????

RE: current phase imbalance

Yes, earlier readings were erroneous.

You never mentioned how were they measured and if the second time measuring method was any different.

Rafiq Bulsara
http://www.srengineersct.com

RE: current phase imbalance

(OP)
Same Greenlee CM-950 clamp on,same conductors,same method.
Also, voltage was normal both times.

RE: current phase imbalance

Did you use a tong-tester / clamp-on ammeter? Tong-testers can produce seemingly inexplicable results if the split cores do not close fully. Normally it's caused by a little bit of dirt which gets on the face of the magnetic core. If it is an ammeter then the readings are wrong - usually low in my experience, but I ain't seen everything smile - and if it is a scope probe then the amplitude and the phase displacement is affected.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: current phase imbalance

Operator error seems the most plausible cause. Happens all the time. I would not scratch my head.

Rafiq Bulsara
http://www.srengineersct.com

RE: current phase imbalance

Yeah, my explanation certainly falls into 'operator error', it's just not an immediately obvious one!
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: current phase imbalance

(OP)
Clamp on meter was used. Same meter was used both times.

RE: current phase imbalance

(OP)
Clamp on meter was used. Same meter was used both times.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources