I am trying to use ARC flash Analysis using ETAP 7.0 , but ETAP has limitation that the source Protective device shall be with in 20 bus from the faulted bus. Can we do the study if the Protective Device is away about 50 bus.
Can we apply arc flash analysis for the distribution overhead lines ? Please suggest

RE: Arc flash study using ETAP

Would you feel safe going in a gear by yourself, if someone tells you, " Don't worry. A device 50 buses upstream (and probably miles away) is protecting you."?

Many things may be possible, but not useful or sensible.

Rafiq Bulsara
http://www.srengineersct.com

RE: Arc flash study using ETAP

Not knowing anything about ETAP, or your system. But the worst case would be at your protection. Then simplify your system to run the study at descrete points.

RE: Arc flash study using ETAP

How in the world do you have 50 buses between the fault and the protective device?  

Are you modeling every pole on a long distribution line as a bus?

RE: Arc flash study using ETAP

Quote:

Can we apply arc flash analysis for the distribution overhead lines ? Please suggest

I believe NESC (National Electrical Safety Code) Article 410 covers arc flash for overhead lines. IEEE 1584 and NFPA 70E covers equipment (enclosed??) up to 15kV. You may want to check with ETAP.

There are some other differences such as the overhead lines considers L-G fault currents vs. 3 phase as in IEEE 1584 and so on.  

Rafiq Bulsara
http://www.srengineersct.com

RE: Arc flash study using ETAP

Quote:

Are you modeling every pole on a long distribution line as a bus?

Possibly, depending on the software and the original intent of the model.  

 

David Castor
www.cvoes.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources