Piping and Valve Materials
i am designing fuel control skids for the Diesel, Natural Gas, Heavy Fuel Oil and some of waste fuel oils.
The pressure and temperature ratings are
Diesel 150psi, 30°C.
Gas 70psi, 30°C
Heavy Fuel Oil 150psi, 200°C.
I need some assistance in decided the right material in each stage of the skids.
i would say the important components for the skids are
1) Manual ball valves
2) Strainers
3) Pressure Regulators
4) Control Valves
5) Pipes
6) Check Valves
7) Pressure Gages
i would like to know what kind of materials i can use, Brass, Stainless steel, cast iron, carbon steel.
i would also like to know ,
when should we use threaded VS flanged?
when should we use welded VS threaded?
please help.
Thanks in advance.
Gas 70psi, 30°C
2) Strainers
4) Control Valves
5) Pipes
6) Check Valves
7) Pressure Gages
please help.
Thanks in advance.
RE: Piping and Valve Materials
Carbon Steel with 150# flanges should be fine for your temps and pressure. Fuel oil is getting close to the limit of the flanges but still under. You might need to check stresses on these sections. I wouldn't use anything that is threaded.
What type of welds you put on your fittings and branches would depend on the size. Fittings anything under 1-1/2" should SW, above should BE.
Valves probably need to have 13% CR trim.
http://engineerhumor.com/
Clarify if these are normal or maximum conditions - and the setting for the process safety relief valves etc. If carbon steel, the fuel oil at 150 psig, 200°C would appear to be in the Class 300 piping system and other fluids appear suitable for Class 150 flanges. You need to check the standards that apply.
You need access to the project standards and the basis for the project design for your area and industry.