How to determine the capacity/strength of bolt? under horizontal & vertical force and moment. Is there any sample application of UBC (Uniform Building Code) in regards to my query? Many thanks..
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Joint Connection
Check tension and shear. Find the allowable stresses (or load factors) for the type of bolt material. Then check combined tension and shear. The ratio of actual to allowable for both added together should not exceed 1.
Depending on the application, the code might require a higher safety factor than allowable stress would imply.
Why are you using the Uniform Building Code? Is this an old application?
Some bolt loads are tabulated and can be found in manuals such as AISC, but those might not be for your application.