Hi,

I am sure you have seen it and done it all. I am not used to electromechanical relays and had my first encounter with them recently. I have a GE PJC32 relay

http://www.gedigitalenergy.com/app/ViewFiles.aspx?prod=pjc&type=3

It is a instantenous relay with a curve charc. Customer has a 250E fuse which does not seem to be coordinating with this 4800A Inst. OC setting.  Could you kindly suggest me any other option interms of electromechanical relay may be Extremely or Very inverse which could replace my Inst O/C relay and still serve the same purpose by providing coordination betweek fuse and O/C relay.

Thanks

RE: GE Electromechanical Relay

GE has several electromechanical time-overcurrent relays. Some have optional instantaneous elements as well. You might try an extremely inverse time characteristic such as the IFC77.

http://www.gedigitalenergy.com/multilin/catalog/ifc.htm

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: GE Electromechanical Relay

Yes it has a curve, but I expect it will not coordinate with a 250 amp fuse....it is just to fast.  I usually expect that there will be no time coordination with the instantaneous relay, ie: if it can "see" the fault current, it will operate irregardless of whether or not a downstream device does as well.

One question would be, do you have other time overcurrent protection installed, and if so do you really need the PJC.

As alehman says you could substitute another relay such as a 77 or slower.  If your PJC is in an S1 case, then any GE IAC relay designed for the S1 case (as most of their old overcurrent relays are) will slide in.  You may need to do some minor wiring on the case to get the time overcurrent output hooked up though.

Alan

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources