Generator influnece to primary side of transformer

Generator influnece to primary side of transformer

Generator influnece to primary side of transformer

(OP)
Last week we had an issue with a short circuit at 150kV grid. This caused the site generator unit trip on a current setting.(3550 Amps registered by the protection relay)
The generator load at that moment was 35 MW, 9 MVAr.
The site load was 25 MW 8 MVAr.
This On site generator is 46 MVA and is supplying 10 kV.
This site grid is behind a transformer 150/10kV 20% Uk.
I don't need the exact numbers, but how is the impedance of the transformer behaving in this situation, while the generator is feeding from 10kV into this primary short circuit, seen from the 10kV side?

regards

BHT
 

RE: Generator influnece to primary side of transformer

No differently than at any other time. It is just a chunk of impedance in the equivalent circuit, no different from any other impedance.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources