Canopy next to a building

Canopy next to a building

Canopy next to a building

(OP)
I have a canopy that is directly adjacent to a building.  The canopy is free standing and there is less than 6" clear between the two.  The building has two elevated stories and roof (approximately 36' building height).  The canopy is about 9'-6" high.  

What would you use for wind loads here?  If I use ASCE 7-05 6.5.13 for open buildings, the uplift is rather small (about 15psf).  If I look at it as a stepped roof as in Fig 6-12, the uplift is around 27psf.  

It won't matter for the actual canopy design, but will make a pretty big difference for the footings.

What have others done for this situation?  

RE: Canopy next to a building

Is the canopy the drive thru type with a sinlge line of cantilevered columns?
Just trying to picture it.

I ususally go with the worst case and weigh my options.
not to undermine your concerns in the least, but an old professor I had used to say "why do engineers love concrete? Because this $!&! is cheap!!!"
 

RE: Canopy next to a building

(OP)
It has only two columns.  It covers a building entrance.  One column on each side of the entrance.  The columns are set roughly 4 ft from the building and the "roof" members cant both toward the building and away from it off of the column.

I agree about the concrete being cheap, but I also would hate to totally overdesigning it needlessly.

RE: Canopy next to a building

Also, a few years ago we got a call to look at the type of canopy I described with a cantilevered roof and columns.
The steel had just been erected and there were already excessive deflections on the roof. The deflections wound up being a culmination of some footing settlement, steel deflections and poor fabrication. It was a disaster.  

RE: Canopy next to a building

I guess I am just trying to offer some advice as to what I have seen. I have only been involved in one project like this and I'm sure the architect and the original structural engineer would have loved a chance at a re-do.
 
The canopy I am describing was curved in plan about 100 feet long, stood about 20' tall and had a roof structure that was cantilevered about 20' as well.  

RE: Canopy next to a building

SEIT...I've done hundreds of these.  I treat them as independent, open structures unless they are physically attached.  Even a 6-inch gap is a large opening to dissipate wind influence.  While there probably is some difference in influence, it would take a wind tunnel model to determine.  I just finished one in a 150 mph wind area.  

I have also treated some of them as overhangs, depending on the configuration.  In most of the applications I deal with, the difference in roof height is a bit much to consider it a stepped roof.

When designing for snow drift, unless there is a separation of several feet, I do consider snow drift against the adjacent building.

RE: Canopy next to a building

I would also calculate the worst case with "h" based on the main building height. In my opinion the building is there and it shouldn't be ignored. If the results of the design aren't crazy I would go with it. The problem comes if the results are too heavy.

The minimum condition that I would consider would be to use the positive wind pressure on the building wall applied as an uplift on the underside of the canopy. I would also add some amount of uplift to the top.

RE: Canopy next to a building

(OP)
Thanks, guys.  I'm going to go with the higher (25 psf) wind.  It only makes the footings go from 3'-6" square to 4'-0" square.

RE: Canopy next to a building

Good call, that extra 6" sure makes your pillow a little softer at night!!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources