Star delta motor on a VFD
How can I wire a star-delta motor ( six lead) to a VFD ? The motor has leads ( U1, V1, W1 , U2, V2 and W2. thanks
RE: Star delta motor on a VFD
Gunnar Englund
www.gke.org
If so, you want to wire it in delta for VFD application.
Rafiq Bulsara
http://www.srengineersct.com
h
Rafiq Bulsara
No offence taken. All information is useful.
I would think dual voltage rating would be posted on the name plate. Perhaps that is what the OP meant by star-delta motor, then what you said is absolutely correct.
If the name plate indicates single voltage and the motor has six leads, it is usually meant for delta. At least that what I had come across in six years of experience in the IEC/India in the 80's. I thought by star-delta motor the OP meant a motor used on a star-delta starter, which probably was not correct.
Rafiq Bulsara
Wire it for the voltage corresponding to your grid voltage.
Gunnar Englund
www.gke.org
NEMA Star:delta is normally used for starting, star to start, delta to run.
Bill
"Why not the best?"
Jimmy Carter
Muthu
www.edison.co.in
Bill
"Why not the best?"
Jimmy Carter