Where can I find some instructions on how and when to derate cable for high altitude applications? It does not seem to be mentioned in the NEC.

RE: Derating Cable for High Altitude / Elevation

I didn't find discussion of altitude in my cable application books either nor on a couple cable websites.

Transformers and switchgear get derated at high altitudes, but I have not seen it done for cables.  It makes sense, the less dense air has less cooling capability, but how much?

RE: Derating Cable for High Altitude / Elevation

Adjustments for altitude of transformers and switchgear are made for insulation dielectric strength, not for loading.  Cable insulation dielectric strength doesn't depend on air pressure.
 

RE: Derating Cable for High Altitude / Elevation

Using different ANSII tables I would derate the current as follows;
1000m = 100%
3000m = 96%
6100m = 90%

This is the current derating for fuses, enclosed air disconnects, metal enclosed and metal clad switchgear. Basically, it accounts for the reduces cooling effect of the less dense air.

As already pointed out, the insulation strength does not depend on air pressure so it would not de-rate. But, any place relying on through air clearances should be derated as follows;
1000m = 100%
3000m = 80%
6100m = 56%

So, say you require 3/8" clearance minimum for 480V. At 6100m this would be very close to 3/4" required.
 

RE: Derating Cable for High Altitude / Elevation

(OP)
Thanks for the answers. I find it sort of surprising that cable derating for elevation does not show up in the NEC or in some other relevant standard. Now I have to use good engineering judgment, and use my not-so-deep wisdom to talk someone into buying bigger by some not-too-clear degree. I might as well go find a brick wall to talk to, without a standard to back me up.

RE: Derating Cable for High Altitude / Elevation

I'd guess that it is not addressed in the NEC because it has never been an actual problem.  Most of the NEC is based on hindsight - fixing problems that have already occurred.  

 

"Theory is when you know all and nothing works. Practice is when all works and nobody knows why. In this case we have put together theory and practice: nothing works... and nobody knows why! (Albert Einstein)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources