Power transformer vibration limits
We have an application with an offshore wind farm substation designed with a monopile giving quite some vibrations in the structure due to wind and waves.
How vulnerable will an e.g. 250MW 33/150kV 50Hz transformer be for such vibrations?
More steel means less requirements to transformer vendor and vice versa. What would be reasonable limits?
Best Regards.
Best Regards.
RE: Power transformer vibration limits
The amount the unit can take will vary depending on manufacturer and type of unit. We have several mobile substations which are bsically a transformer that is mounted to a trailer and is transported every couple of months for it's entire lifetime. The vibrations from running down the less than perfectly paved roads do not seem to affect the units at all, but then they were designed for it.
If it is broken, fix it. If it isn't broken, I'll soon fix that.
Are you saying that the substation is going to be installed on an offshore platform? Or is the substation going to be on the shoreline, and you are concerned about the vibrations from the waves crashing into the shore?
The design is ongoing, but data on similar projects shows 0,37-0,38 Hz with RMS displacement of 0,053m and peak displacement of 0,462m (100 years).
I expect a ordinary core form transformer, and it has to be powered when it vibrates.
Best regards
Are there any IEC or other standards dealing with vibrations?
Make a big assumption that the vibration is roughly sinusoidal ... sinusoidal amplitude may change over time but on a time scale much longer than the period of the sinusoid.
sinusoidal vibration at 0.38hz which has an rms displacement of 0.462m rms would have a peak/0 acceleration of 0.4 g's.
I have seen large GSU's shipped on a truck – the limit for acceleration for the impact recorder was 5 g's... agreed by the OEM.
On that basis, I would think it is not a problem. But that's just a quick look, and need to check the assumption.
1 - damage due to infrequent high-magnitude accleration
2 - fatigue or loosening due to long-term low-level vibrations.
My comments above addressed only the first.
It might be worth the time to get someone inside the transformer and add a second nut to all of the threads. This is what we do with our mobile units to ensure nothing comes loose.
If it is a concern, you could mount the transformer on an air lift platform similar to a truck trailer suspension system. truck trailer air bags would do the trick. You would need to make a solid base supported in several places by airbags. I would think you'd need about 20 bags for a transformer of that size. These would help absorb some of the impacts. I would work similar to the suspensions system in your car. This would be more for large impacts, though it could help with the vibration issue.
How did u do this mathematics of accelration in g's.
f = frequency = 0.38hz
w = radian frequency = 2*pi*0.38 sec^-1
Write expression for displacement d(t)
d(t)=sqrt(2)* 0.462 * sin(w*t) meters
Compute velocity v(t) as derivative of displacement d(t)
v(t) = d/dt{d(t)} = w * sqrt(2)*0.462*cos(w*t) meters
Compute acceleration a(t) as derivative of velocity v(t)
a(t) = d/dt{v(t)} = w^2 * sqrt(2)*0.462*cos(w*t) meters
Substitute w = 2*pi*0.38 sec^-1
a(t) = (2*pi*0.38 sec^-1)^2 * sqrt(2)*0.462*sin(w*t) meters
Move units to the end
a(t) = (2*pi*0.38)^2 * sqrt(2)*0.462*sin(w*t) meters/sec^2
Multiply by g*sec^2/(9.8*m^2)=1
a(t) = -(2*pi*0.38)^2 * sqrt(2)*0.462*sin(w*t) meters/sec^2 * g*sec^2/(9.8*meter)
Cancel units
a(t) = -(2*pi*0.38)^2 * sqrt(2)*0.462*sin(w*t) g / (9.8)
Rearrange all numerical factors to the front
a(t) = -[(2*pi*0.38)^2 * sqrt(2)*0.462 /9.8] * sin(w*t) g's
Solve [ ]
a(t) = -[0.38] * sin(w*t) g's
peak value of a(t) is 0.38 g's
Here is an application note on converting vibration units (handy for rotating equipment vibration conversions)
http://www.reliabilitydirect.com/appnotes/cvr.html
Also there are vsiour programs to perform these conversions Here is one for free:
http://www.wilcoxon.com/knowdesk_VibCalc.cfm
Attached is a spreadsheet I wrote for the same purpose