ac induction motor
ac induction motor
(OP)
Curiously what are the implications of operating these motors in their service factor and at 50%,100% loads and in overload.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: ac induction motor
RE: ac induction motor
except I didn't know what you meant by "The motor may or may not run cooler at reduced load". To my knowledge decreasing load always decreases temperature. No-load losses are at most approx 60% of total losses. The remaining losses (load losses) vary approx with the square of load.
RE: ac induction motor
RE: ac induction motor
Curiously what are the implications of operating these motors in their service factor
///If you follow NEMA MG-1 statement, the motor will have shorter lifecycle. However, the motor can be built to operate within overload condition corresponding service factor and it can outlast its identically rated motor with the same service factor, e.g. SF=1.15, continuously operating at SF=1.0 or lower. This is may be difficult to understand; however, the motor life-cycle in continuous operation depends how the manufacturer builds it. This is somewhat similar to the inverter duty motors.\\\
and at 50%,
///Efficiency low, power factor may be somewhat higher or lower (it just depends on the motor design), lifecycle higher, slip small, etc.\\\
100% loads
///The motor rated parameters should prevail, depending on the motor manufacturing tolerances.\\\
and in overload.
///It just depends on how big overload. It can potentially burn.\\\
RE: ac induction motor