11 kv/400 v transformer phase problem !!

11 kv/400 v transformer phase problem !!

11 kv/400 v transformer phase problem !!

(OP)

we faced a problem in power plant consisted of 4 diesel generators 400 v synchronise togather and every generator connected to 400v/11kv delta/wye Transformer the synchronisation in low voltage side (400v) when we turn on the first generator it's transformer rise up the voltage to 11kv and this voltage delivered to all transformers in the high voltage side (11kv) but in each low voltage sides of each transformer there's only two phases live and the other one have 0 voltage ( we tested by voltmeter ) we tried by starting from other generator but it's the same problem. all the for transformers act like that (when we feed it from low voltage side it work perfectly but when we feed it from high voltage side there's missing phase in the other side (400)!!  ... could u help me plzzz ???

RE: 11 kv/400 v transformer phase problem !!

You do have an insulated N, I assume. Are you testing voltage from that N or from Ground?  

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: 11 kv/400 v transformer phase problem !!

Assuming that the 400V is on the delta side of the transformers, the only meaningful voltage measurements are from phase to phase.

RE: 11 kv/400 v transformer phase problem !!

(OP)
i tested it according to the ground and according to the other phase even i touch it by bare hand and bare feet !!! it's voltage 0 zero... that's really make me sick :(

RE: 11 kv/400 v transformer phase problem !!

Quote:

i tested it according to the ground and according to the other phase even i touch it by bare hand and bare feet !!! it's voltage 0 zero... that's really make me sick :(
First of all, touching with your bare hands is liable to make you dead, not just sick!!

As David said, measuring from phase to ground without the generators running is not meaningful.  The generators provide the only ground source, so when they are not running, there is no defined voltage from phase to ground.  Measure the phase-to-phase voltages.

RE: 11 kv/400 v transformer phase problem !!

(OP)
as well as every generator sensing missed phase .... low voltage side for every transformer is delta

RE: 11 kv/400 v transformer phase problem !!

It's possible that one phase of your generators are intentionally grounded, although that would be unusual.

As others have said, you you measured phase to phase with a volt meter? (not your fingers!)

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: 11 kv/400 v transformer phase problem !!

I would be checking the connections on the synchroscope.
It is possible that someone used 240:120 PTs, phase to ground for the synchroscope rather than 400:120 PTs phase to phase.
That would probably give the symptoms as I understand them on an ungrounded delta system.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 11 kv/400 v transformer phase problem !!

(OP)
actually the terberg "synch. module" phase voltages was L1=0,L2=680,L3=400 but i measured it by voltmeter: L1L2=400,L2L3=400,L1L3=400 .... and according to ground
L1=0,L2=400,L3=400 !!! does any one tell me y this transformer act like that ??!!  

RE: 11 kv/400 v transformer phase problem !!

Quote:

does any one tell me y this transformer act like that ??!!
Several respondents have already - there is no ground source.

RE: 11 kv/400 v transformer phase problem !!

Actually, it sounds like a corner grounded delta system.  Don't use any voltages other than phase-phase, none of the rest mean anything.

RE: 11 kv/400 v transformer phase problem !!

One phase has a connection to ground in each transformer. Probably a PT for the synchroscope connected to ground.
Other than that, look for some device that each transformer LV side has that is connected to ground in each instance.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources