LOCATION OF FIRE ALARM PANEL
Can someone refer to the NFPA cluase where i can find where to locate the fire alarm panel, i mean at the ground floor or could it be located at upper levels and if the hight of the building has any relation to that ?
Elecme
RE: LOCATION OF FIRE ALARM PANEL
There is often a requirement for a fire alarm annunciator to be located at an outside entrance on larger (taller) buildings.
Just as a mattewr of interest BS5839 (UK) requires location to be in immediate vicinity of entrance. Multiple entrances will require repeater panels.
Lyledunn
http://www.nfpa.org
http://www.silentknight.com/pdffiles/Firepdf/2224pdf/2224spec.pdf
http://www.dal.ca/~ehs/part3.htm
http://www.honeywell.com.pl/pdf/automatyka_budynkow/pozary/EN-0822R0.pdf
for more info
Also, check the local laws that may be stricter than NFPA.