EPRI Red Book 3rd Edition.
I would like to know if EPRI Red Book 3rd edition is worth having a look at because I have seen that it has a huge price.
Does anybody know if it is available in any university library? Due to its high price I discard buying it but as I am a lecturer in a university, I could ask for an interlibrary loan.
Thanks.
Thanks.
RE: EPRI Red Book 3rd Edition.
May you grow up to be righteous, may you grow up to be true...
Hope this helps.
Sorry for the long post:)
Chapter 1
Transmission Systems
1.1 INTRODUCTION
Background
Transmission System Characteristics
Industry Trends Affecting Line Design
Feedback of Experience
Organization of this Chapter
1.2 ELECTRICAL DESIGN
Voltage, Impedance and Power Limit
Standing Waves
Transients
1.3 ENVIRONMENTAL CONSIDERATIONS
The Impact of a Line on the Environment
The Impact of the Environment on a Line
1.4 TRENDS IN THE ELECTRICITY
SUPPLY INDUSTRY 1
Generation
Transmission
Distribution
Overall Impact
1.5 FUTURE DIRECTION OF THE ELECTRICITY
SUPPLY INDUSTRY
Technical Strategies
Specific Issues to be Addressed
1.6 LEGISLATIVE AND REGULATORY ISSUES
Introduction
Examples of Inadequate Planning
Regulatory Framework and Process for Transmission-Line Permitting
Primary Issues for Transmission-Line Permitting
New or Expanding Issues
1.7 COMPARISON OF THE THIRD EDITION OF THE REFERENCE BOOK TO THE SECOND EDITION
1.8 CONCLUSIONS
Chapter 2
Electrical Characteristics of Conductor Configurations and Circuits
2.1 INTRODUCTION
2.2 BARE CONDUCTORS FOR
OVERHEAD TRANSMISSION LINES
Conductor Materials
Areas and Diameter
Weight and Rated Strength
Electrical Resistance
GMR of Stranded Conductors
Inductive and Capacitive Reactance "to One Meter (Foot)"
Annealing of Aluminum Stranded Conductors
Sag Tension of Overhead Lines
Thermal Rating (Ampacity) of Bare Conductor
Transient Thermal Ratings
2.3 CONDUCTOR SURFACE GRADIENTS
Introduction and Overview
Single Conductor
Multiple Conductors
Conductor Bundling
Toroidal Shielding Electrodes (Corona Rings)
Variation of Surface Gradient with Design Parameters—Applets and Examples
2.4 BASIC TRANSMISSION LINE IMPEDANCE AND ADMITTANCE PARAMETERS
Introduction
Positive Sequence Inductive Reactance
Positive Sequence Capacitive Reactance
Surge Impedance and Surge Impedance Loading
2.5 GENERAL TRANSMISSION-LINE PARAMETERS
Capacitive (Electric Field) Unbalance
Single-Circuit Inductive (Magnetic Field) Unbalance
Unbalance in Parallel Double-Circuit
Untransposed Lines
2.6 INDUCED VOLTAGES ON PARALLEL
CONDUCTORS
Electric Field Induction on the De-Energized Circuit
Magnetic Field Induction on the De-Energized Circuit
Appendix 2.1 ELECTRICAL AND MECHANICAL
CHARACTERISTICS OF CONDUCTORS
Chapter 3
Insulation Design
3.1 INTRODUCTION
Definition
Design Factors for Transmission Lines
Critical Factors versus Stress Type
Design Optimization
Calculation Methodology
Typical Performance Criteria and Design Clearances
Applets
Summary
Layout of this Chapter
3.2 VOLTAGE AND ENVIRONMENTAL STRESSES ON TRANSMISSION LINES
Introduction
Lightning
Switching Surges
Temporary Overvoltages
Environmental Stress
Summary
3.3 INSULATION STRENGTH
Introduction
Lightning Impulse Strength
Switching Impulse Strength
Power Frequency Strength
Effect of Weather Conditions
Summary
3.4 OVERVOLTAGE CONTROL
Introduction
Control of Lightning Overvoltages
Control of Switching Surges
Control of Power Frequency Stress Caused by Insulator Contamination
Summary
3.5 ELECTRIC SAFETY CODE REQUIREMENTS
Introduction
National Electric Safety Code (NESC 2002)
Clearance Requirements
Summary
3.6 COORDINATION OF DESIGN REQUIREMENTS
Introduction
Insulation Coordination Analysis Methods
Lightning Performance of Transmission Lines
Switching Surge Performance of Transmission Lines
Power Frequency Performance of Transmission Lines
Consolidation of Design Requirements
Alternate Method for Line Design: Storm Outage Rate
3.7 ECONOMIC CONSIDERATIONS
Introduction
Insulation Coordination and Cost
Line Component Costs
Cost Sensitivities
Independent Cost Items
Base Line Costs
Cost Analysis Methods
Appendix 3.1 INSULATION COORDINATION ANALYSIS TOOLS
Appendix 3.2 SURGE ARRESTER APPLICATIONS ON TRANSMISSION SYSTEMS: STATION AND LINE ARRESTERS
Appendix 3.3 INSULATION COORDINATION METHODOLOGIES
Appendix 3.4 APPLICATION OF INSULATION COORDINATION ACCORDING
TO IEC 71-2 INSULATION COORDINATION
Chapter 4
Insulation for Power Frequency Voltage
4.1 INTRODUCTION
4.2 INSULATOR TECHNOLOGY
Historical Perspective
General Insulator Terms and Classification
Hydrophobicity
Components of Ceramic and Glass Insulators
Components of Polymer Insulators
4.3 THE MECHANISM OF CONTAMINATION FLASHOVER
Introduction
Buildup of Contaminants on Insulator Surfaces
Wetting Processes
Discharge Activity and Development of Flashover
4.4 LONG-TERM PERFORMANCE OF INSULATORS
Causes of Degradation and Damage
Porcelain and Glass Insulators
Polymer Insulators
4.5 LABORATORY TESTING
Introduction
Test Methods to Determine the Long-Term Performance of Insulators (Aging Tests)
Contamination Flashover Tests
4.6 ELECTRICAL PERFORMANCE OF INSULATORS AND AIR GAPS UNDER AC VOLTAGE
Dry and Wet AC Flashover Strength of Air Gaps and Insulators
Contamination Flashover Performance of Insulators
Glass and Porcelain Insulators
Polymer Insulators
Resistive Glaze Insulators
4.7 PERFORMANCE OF INSULATORS IN FREEZING CONDITIONS
Clean- and Cold-Fog Test Results
Icing Test Results
Snow Test Results
4.8 INSULATION DESIGN
Introduction
Characterizing the Environment and its Severity
Choice of Material
Flashover Probability of Contaminated Insulators
The Insulator Dimensioning Process
4.9 ELECTRIC FIELD ON INSULATORS ANDGRADING RINGS
E-Field Distribution on Polymer Insulators
E-Field Distribution on Glass and Porcelain Insulator Strings
Appendix 4.1 INSULATOR TYPES REFERRED TO IN THIS CHAPTER
Chapter 5
5.1 INTRODUCTION
5.2 PRINCIPAL VARIABLES IN SWITCHING SURGE FLASHOVER
Switching Surges and Switching Impulses
Switching Impulse Polarity
Switching Impulse Waveshape
Influence of Geometry on Switching Impulse Strength
Meteorological Influence on Switching Impulse Strength
Statistical Fluctuations in Switching Impulse Strength
5.3 FLASHOVER MECHANISM
5.4 SWITCHING IMPULSE TESTING TECHNIQUES
Switching Impulse Generators, Test Circuits, Test Objects
Test Methods 5-12
5.5 SWITCHING IMPULSE STRENGTH OF SIMPLE AIR GAPS
Rod-Plane
Vertical Rod-Rod
Horizontal Rod-Rod
Sphere-Plane
5.6 SWITCHING IMPULSE STRENGTH OF LINE INSULATION
Tower Window
Outside Phase
Insulator Strings
Conductor-to-Tower Leg
Conductor-to-Grounded Objects at Midspan
Anomalous Flashovers
5.7 SWITCHING IMPULSE STRENGTH OF STATION INSULATION
Horizontal Insulator Strings
Station Post Insulators
5.8 PHASE-TO-PHASE SWITCHING SURGE STRENGTH
Phase-to-Phase Strength for a Horizontal Rod-Rod
Phase-to-Phase Strength of the Air Gap Between Conductors
Phase-to-Phase Strength of Other
Insulation Geometries
Phase-to-Phase Insulation Stress
Design of Phase-to-Phase Gap Length
5.9 VARIATION OF FLASHOVER PROBABILITY WITH VOLTAGE
Withstand Voltage Level
5.10 EFFECT OF WAVESHAPE ON SWITCHING IMPULSE STRENGTH
5.11 EFFECT OF AIR DENSITY AND HUMIDITY ON SWITCHING IMPULSE STRENGTH: CORRECTION
TO STANDARD CONDITIONS
Standard Air Density and Humidity Conditions
Effect of Air Density
Effect of Humidity
5.12 EFFECT OF RAIN AND OTHER WET WEATHER CONDITIONS ON SWITCHING IMPULSE STRENGTH
Air Gaps and Clean Insulators
Switching Impulse Strength of Contaminated Insulators
5.13 RISK OF FAILURE OF PHASE-TO-GROUND INSULATION
Distribution of Switching Surges on Transmission Lines
Parameters Affecting Risk of Failure Caused by Switching Surges
Simplified Design Procedure
5.14 CONSIDERATION OF SWITCHING SURGES DURING LIVE-LINE MAINTENANCE
Minimum Number of Insulators to Withstand Switching Surges
Performance of Portable Protective Gaps
Effect of Floating Objects
Appendix 5.1 COMPUTATION OF THE SWING
ANGLE DISTRIBUTION
Appendix 5.2 MODEL FOR THE CALCULATION OF SWITCHING IMPULSE STRENGTH
OF AIR GAPS
Chapter 6
Lightning and Grounding
6.1 INTRODUCTION
Historical Context
Lightning Protection of Transmission Lines
Simulation of Lightning on Transmission Lines
Capital Cost of Lightning Protection for Transmission Systems
Benchmark: Cost of Avoided Momentary Outages
Organization and Contents of the Chapter
6.2 THE LIGHTNING FLASH
Cloud Electrification
The Stroke Mechanism—Negative Downward Leaders
The Stroke Mechanism—Upward Positive Leaders
The Stroke Mechanism—Positive Flashes
Charge and Voltage
Leader Diameter, Visibility, and Branching
Structure and Progression of the Positive Upward Connecting Leader
First Return Stroke Waveshapes
First Negative Return Stroke Parameter Distributions
Positive Return Stroke Parameter Distributions
Subsequent Stroke Parameters
Electromagnetic Fields from Return Strokes
Upward Flashes from Tall Structures
Experience on 60–140 m Towers
Winter Lightning
Arc Damage from Flash Charge
6.3 REGIONAL LIGHTNING FLASH STATISTICS AND DATA
Isokeraunic Maps, OTD Measurements, and Lightning Flash Counters
General Observations
The North American Lightning Detection Network
Inter-comparison of Lightning Detection Methods
6.4 SURGE IMPEDANCE AND CORONA EFFECTS
Surge Impedance of Single Wires and Bundles
Surge Impedance of Towers
Calculation of Insulator Voltage and Lightning Performance
6.5 INSULATION STRENGTH FOR LIGHTNING IMPULSES
Volt-Time Curve Penetration Algorithm, Evaluated at Span Reflection Time
The Disruptive Effect (DE) Algorithm, Typically for Faster-Front Flashover/Puncture
The Leader Progression Model, Typically Evaluated for Several Span Reflection Times
Insulator Puncture Strength
6.6 SHIELDING FAILURE CALCULATIONS
The Shielding Failure Process
Uncovered Areas in the Shielding Failure Models
Recommended Strike Distance Equations
Perfect Shielding
The Method of Maximum Heights
Cascading Flashovers
Transmitted Stress to Terminals
Calculation Procedures
Simplified Models
6.7 INITIATION OF BACKFLASHOVERS
The Backflashover Process
Dynamic Models for Electrical Insulation Strength
Digital Models for Backflashover
Applet Descriptions
6.8 INITIATION OF INDUCED FLASHOVERS
Induction from EM Fields of the Lightning Flash
Simplified Model for Induced Overvoltages
Protection against Induced Flashovers
Importance for Subtransmission and Underbuilt Distribution
6.9 INITIATION OF MIDSPAN FLASHOVERS
The Failure Mechanism
Corona Coupling at Midspan
Current Injection into Phase Conductors
Tower Flashovers Caused by Midspan Strokes
Cascading Flashovers at Adjacent Structures
Rules for Midspan Spacing
6.10 TRANSMISSION-LINE GROUNDING
Mechanical Integrity
Guy Anchors for Additional Strength
Corrosion and End-of-Life Aspects
Steady-State Tower Potentials
Earth Resistivity—Its Importance and Measurement
Influence on Dielectric Strength of Soils
Vertical and Horizontal Layering
Measurement Techniques and Typical Results of Field Tests
Capacitance, Electrolytic and Dielectric Effects
Dynamics of Ground Resistance
(Applets L-1 and L-3)
Nonlinear Dynamics of Ground Rods
The Liew-Darveniza Calculation of Rod Dynamic Resistances
Use of the Korsuncev Criterial Curve
Metal Tower and Reinforced Concrete Foundations
Radial and Continuous Counterpoise
Recommendations for Line Flashover Calculations
Step, Touch and Transferred Potentials
Coordination With Safe Body Withstand Levels
Calculation of Surface Potentials Using L-6 Applet
Appendix 6.1 THEORY OF THE DISRUPTIVE EFFECT ALGORITHM
Appendix 6.2 ELECTROMAGNETIC FIELDS FROM LIGHTNING
Chapter 7
Electric and Magnetic Fields
7.1 INTRODUCTION
7.2 BASIC ELECTRIC AND MAGNETIC FIELD PRINCIPLES
EMF: Electric and Magnetic Fields
Phasors and Vectors
Electric Field
Magnetic Fields
7.3 CALCULATION OF ELECTRIC FIELDS
General Method for Transmission Lines
Lateral Profile of Electric Field at Ground Level
Maximum Electric Field at Ground – Generalized Curves
Effect of Line Parameters
Electric Field of Double-Circuit Lines
Electric Field in Substations
7.4 CALCULATION OF MAGNETIC FIELDS
Example Calculation
Calculation of Magnetic Field from Power Lines Using Simple Equations
Calculation of Magnetic Field from Sets of Conductors in Three Dimensions
7.5 MEASUREMENT OF ELECTRIC FIELDS
Techniques for Measuring the Unperturbed Electric Field
Measurement of the Electric Field on a Boundary Surface
Measurement of the Space Potential
7.6 MEASUREMENT OF MAGNETIC FIELDS
Magnetic Field Meters
Measurement of Magnetic Field from Power Lines
Waveform Capture Instrumentation
7.7 COMPARISON BETWEEN HV TRANSMISSION-LINE AND COMMON ENVIRONMENT ELECTRIC
AND MAGNETIC FIELDS
7.8 ELECTRIC FIELD INDUCTION IN OBJECTS
Electrical Parameters of Objects with Different Shapes
Accuracy Expected in Calculating Short-Circuit Currents
Electric Field Induction in Long Objects in a Nonuniform Electric Field
Impedance of Vehicles to Ground
7.9 MAGNETIC FIELD INDUCTION IN OBJECTS
Short-Circuit Currents and Open-Circuit Voltages of Sets of Conductors Parallel to Transmission Lines
Shield Wire Currents
7.10 RESPONSE OF PEOPLE TO TRANSMISSION-LINE FIELDS
Induced Currents and Their Distribution
Field Enhancement on the Surface of the Body
Currents Induced by Spark Discharges
Transient Currents Induced by Switching Surges
People Response to Short-Term Exposure to Electric Field
7.11 BIOLOGICAL EFFECTS OF ELECTRIC FIELDS
7.12 CURRENTS INDUCED IN THE HUMAN BODY BY TRANSMISSION LINE MAGNETIC FIELDS AND
A COMPARISON WITH THOSE INDUCED BY ELECTRIC FIELDS
7.13 BIOLOGICAL EFFECTS OF MAGNETIC FIELDS
7.14 FUEL IGNITION
Fuel Ignition Caused by Spark Discharges
Corona-Induced Fuel Ignition
7.15 EFFECTS OF HIGH-INTENSITY ELECTRIC FIELDS
Wood Pole Burning
Dead Tree Burning
Tree Tip Damage
Corona on Grounded Objects
7.16 METHODS FOR REDUCING TRANSMISSION-LINE ELECTRIC FIELDS
Introduction—Passive and Active Shielding
Shielding by a Horizontal Grid of Grounded Wires
Shielding By a Vertical Grid of Grounded Wires
Shield Wire Mesh
Shielding by Objects
Effect of Underbuilt Lines on Electric Field (Active Shielding)
7.17 METHODS FOR REDUCING TRANSMISSION-LINE MAGNETIC FIELDS
Line Design for Low Magnetic Field
Optimization of Line Parameters
Line Compaction
Split-Phase Lines
Passive Shielding of Transmission Line Magnetic Field Using Cancellation Loops
Example of Cancellation Loops Applied to a 345-kV Corridor
Fourth-Wire Scheme
Appendix 7.1 CALCULATION OF FIELD ELLIPSE PARAMETERS
Appendix 7.2 USE OF TWO-DIMENSIONAL DIPOLES AND QUADRUPOLES
FOR CALCULATING TRANSMISSION-LINE MAGNETIC FIELDS
Appendix 7.3 STANDARDS AND GUIDELINES
Appendix 7.4 MONITOR JITTER CAUSED BY TRANSMISSION-LINE MAGNETIC FIELDS
Appendix 7.5 MAGNETIC INDUCTION WITH RESISTIVE GROUND RETURN
Appendix 7.6 ELECTRIC FIELD CALCULATIONS FOR THREE-DIMENSIONAL GEOMETRY
Chapter 8
Corona and Gap Discharge Phenomena
8.1 INTRODUCTION
8.2 MECHANISM OF CORONA DISCHARGES
Basic Discharge Physics
Discharges in Uniform Fields
Discharges in Nonuniform Fields
Modes of Corona Discharge
8.3 GAP DISCHARGES
8.4 CORONA ONSET ON CONDUCTORS AND HARDWARE
Conductors
Hardware
8.5 CORONA EFFECTS
Corona Loss
Electromagnetic Interference
Audible Noise
Ozone and NOX
Light Emission
Electrical Wind and Corona-Induced Vibrations
Other Effects
8.6 FACTORS INFLUENCING CORONA PERFORMANCE
Fair Weather Corona Sources
Conductor Surface Conditions
Influence of Water on Conductors
Influence of Weather Conditions
Influence of Conductor Heating
Statistical Consideration of Corona Performance
8.7 GENERATION QUANTITIES OF CORONA EFFECTS
General Principles of Corona Testing
Generated Corona Loss
Radio Noise Excitation Function
Generated Acoustic Power Density
8.8 CORONA ATTENUATION OF POWER SYSTEM OVERVOLTAGES
Switching Overvoltages
Appendix 8.1 GUIDELINES FOR CORONA TESTING OF HARDWARE
Appendix 8.2 CURRENTS INDUCED BY MOVING CHARGED PARTICLES
Chapter 9
9.1 INTRODUCTION
9.2 CHARACTERISTICS OF TRANSMISSION-LINE EMI
EMI Due to Conductor Corona
EMI Due to Hardware Corona
Gap Discharge EMI
9.3 DESIGN CONSIDERATIONS AND EMI GUIDELINES AND LIMITS
EMI Tolerability Criteria
Design Guidelines and Limits
9.4 MEASUREMENT OF EMI
EMI Instrumentation
Weighting Circuits
Meter Response – Bandwidth and Pulse Repetition Rate
Actual Band-Pass Characteristics
Antenna Systems
Measurement of Transmission-line EMI
Pre-construction, Pre-energization and Post-energization Measurements
9.5 CALCULATION OF EMI FROM CONDUCTOR CORONA BELOW 30 MHZ
Philosophy of Modeling
Analytical Methods
Empirical Methods
9.6 CALCULATION OF EMI FROM CONDUCTOR CORONA ABOVE 30 MHZ
Analytical Methods
Empirical Methods
Calculation of TVI – Low VHF Band
9.7 PASSIVE INTERFERENCE
AM Broadcast Reradiation
TV Broadcast Reradiation
Appendix 9.1 CALCULATION OF CORONA-INDUCED CURRENT ON PHASE CONDUCTORS
Appendix 9.2 STATISTICAL AVERAGES
Appendix 9.3 EVALUATION OF INVERSE SPATIAL TRANSFORMS
Appendix 9.4 APPROXIMATIONS FOR Fey, Fhx, AND Fez
Appendix 9.5 GROUND CONDUCTIVITY
Chapter 10
Audible Noise
10.1 INTRODUCTION
10.2 CHARACTERISTICS OF TRANSMISSION-LINE NOISE
10.3 AUDIBLE NOISE AS A DESIGN FACTOR
Effect of Weather Conditions and Load Current
Effect of Line Geometry and Conductor Surface Conditions
Audible Noise from Insulators and Fittings
10.4 CALCULATION OF TRANSMISSION-LINE AUDIBLE NOISE
Generation and Propagation of Audible Noise
Calculation of A-Weighted Audible Noise-Levels in Rain
Audible Noise in Fair Weather
Influence of Tower, Sag, and Ground Wires
Effect of Rain Rate
Effect of Conductor Aging
Effect of Altitude above Sea Level
Effect of Bundle Orientation
Comparison of Audible-Noise Calculation Methods with Measured Data (Rain)
Generation and Calculation of Hum
10.5 MEASUREMENT OF AUDIBLE NOISE
Sound Pressure, Sound-Pressure Level, the Decibel
Weighted Sound Level
Statistical Descriptors
Leq, Ldn and CNEL
Instrumentation
Measurements
10.6 ASSESSING THE IMPACT OF TRANSMISSION-LINE AUDIBLE NOISE— AUDIBLE-NOISE REGULATIONS
Noise Evaluation Studies
Noise Ordinances—United States
Case Study: Example of Limits Based on Any One Hour
Case Study: Example of Limits Based on Some Variation of the EPA "Levels Document"
Case Study: Example of Limits Based on South African Noise Code
10.7 AUDIBLE-NOISE REDUCTION TECHNIQUES
Bundle Geometry Optimization
Other Techniques of Audible Noise Reduction
Appendix 10.1 ADJUSTMENT OF MEASURED AUDIBLE-NOISE LEVELS TO ACCOUNT FOR AMBIENT NOISE INTRUSIONS
Appendix 10.2 AMBIENT NOISE DURING RAIN
Chapter 11
Corona Loss and Ozone
11.1 INTRODUCTION
11.2 PHYSICAL MECHANISM OF CORONA LOSS
11.3 MEASUREMENT OF CORONA LOSS
11.4 CORONA LOSS IN FAIR WEATHER
11.5 CORONA LOSS IN FOUL WEATHER
Corona Losses in Rain
Corona Losses in Snow, Ice, and Hoarfrost
11.6 EFFECT OF ALTITUDE ON CORONA LOSS
11.7 EVALUATION OF CORONA LOSS
11.8 INFLUENCE OF CORONA LOSSES ON LINE DESIGN
11.9 OZONE AND NOX
Mechanism of Generation
Rates of Generation
Ozone Dispersion from Transmission Lines
Ozone Levels Near Transmission Lines
Standards for Ambient Ozone Levels
Chapter 12
Shared Use of the Right-of-Way
12.1 INTRODUCTION
EMC Regulations, Standards and Guidelines
Elements of EMC
Electric Power Transmission-Line Sources
Coupling Paths
Receptors
12.2 INTERFERENCE WITH THE OPERATION OF RAILROADS
Introduction to Coupling Mechanisms between Power Lines and Railroads
Electric-Field (Capacitive) Induction
Magnetic-Field (Inductive) Induction
Conductive (Resistive) Induction
Common and Differential Modes
Coupling between Common and Differential Modes
Overview of Railroad Signaling
Abnormal Operation of Railroad Equipment
Damage to Railroad Equipment 1
Personnel Safety Considerations (Steady-State Operation)
Personnel Safety Considerations (Fault Conditions)
"Rules of Thumb" of Railroad Signals and AC Interference
12.3 INTERFERENCE WITH THE OPERATION OF PIPELINES
Electric-Field Induction
Magnetic-Field Induction
Conductive Coupling
Damage to Pipelines
Personnel Safety
12.4 INTERFERENCE WITH THE OPERATION OF POWER LINE COMMUNICATION SYSTEMS
Power Line Carrier
High-Speed Communications
12.5 INTERFERENCE WITH THE OPERATION OF OPTICAL FIBER COMMUNICATIONS
Comparison of OPGW, ADSS, and WRAP
Experience with WRAP
OPGW EMC Issues
ADSS EMC Issues
12.6 CONSEQUENCES OF INSTALLING COMMUNICATION SYSTEM ANTENNAS ON TRANSMISSION-LINE
TOWERS
Influence of the Power Line on the Antenna
Issues Relating to Grounding and Low-Voltage Feeds
Exposure to RF Electromagnetic Fields
12.7 INTERFERENCE WITH THE OPERATION OF SYSTEMS FOR WARNING AIRCRAFT
Warning Lights
Airway Marking Balls
12.8 INTERFERENCE WITH THE OPERATION OF TELEPHONE SYSTEMS
Telephone Lines
Cordless Phones
Cell Phones
12.9 CONSEQUENCES OF INSTALLING DISTRIBUTION LINES UNDER TRANSMISSION LINES
12.10 INTERFERENCE WITH THE OPERATION OF RADIO NAVIGATION SYSTEMS
LORAN-C
Instrument Landing Systems (ILS)
Global Positioning System (GPS)
Differential Global Positioning System (DGPS)
12.11 INTERFERENCE WITH THE OPERATION OF COMMUNICATION RECEIVERS
12.12 IMPACTS ON AGRICULTURAL OPERATIONS NEAR TRANSMISSION LINES
Operation of Irrigation Equipment
Interference with Cornering Guidance Systems
12.13 USE OF VEHICLES AND LARGE EQUIPMENT NEAR TRANSMISSION LINES
Induced Currents from Vehicles
Spark Discharges (Induced Voltages) from Vehicles
Fuel Ignition
Parking Lots
12.14 IMPACTS ON BUILDINGS NEAR TRANSMISSION LINES
12.15 IMPACTS ON PUBLIC USE OF RIGHTS-OF-WAY
Exposure Guidelines for the General Public
Nuisance Shocks
Open-Space Uses of the Right-of-Way
12.16 AVIAN INTERACTIONS WITH TRANSMISSION LINES
Bird Electrocutions
Bird Collisions
Nesting Issues—Structural
Nesting Issues—Electrical
Nesting Issues—Legal
Nesting Issues—Liability
Bird Pollution
Bird Streamers
Other Bird Issues
Chapter 13
Considerations for Inspection and Maintainability
13.1 INTRODUCTION
13.2 DESIGNING FOR INSPECTION AND MAINTAINABILITY
Designing for Durability and Longevity
Design Examples
13.3 OPTIMIZING THE DESIGN FOR EFFECTIVE LIVE WORKING
Brief Overview of Live Working (LW)
Design and Construction Aspects Important to LW
Low-Cost-Impact Design Modifications That Help Facilitate LW
High-Cost-Impact Design Modifications That Help Facilitate LW
Examples and Lessons Learned
Determining Whether a Line is Maintainable Using LW Methods
Chapter 14
Voltage Upgrading of Existing Transmission Lines
14.1 INTRODUCTION
14.2 SYSTEM LEVEL STUDY OF POWER FLOW NEED AND VOLTAGE STRATEGY
Reactance Limits, Stability, and Surge Impedance Loading
Voltage Drop
Thermal Uprating
14.3 ASSESSING ELECTRICAL FEASIBILITY
Data Gathering
Review of Line Design
Electrical Clearances and Right-of-Way
Review of Electrical Design Criteria
Insulation and Conductor to Structure Clearances
Corona and Field Effects
Grounding and Bonding
14.4 ASSESSING MECHANICAL FEASIBILITY
Mechanical Data Gathering
Review of Original Structure Loads
Sag-tension Calculations
Hardware/Connectors
Insulator Strength
Structure Phase Geometry
Shield Wires
Right-of-Way
Wind and Ice-Induced Conductor Motions
14.5 EVALUATION OF PRESENT LINE CONDITION
Physical Examination
Historical Damage Report Examination
14.6 DETAILED ENGINEERING DESIGN FOR VOLTAGE UPGRADING
Detailed Review of Criteria Applied to Upgrading
Power Frequency Insulation
Switching Surge
Lightning
Structural Analysis and Reinforcement
Detailed Economic Review
Maintenance and Minimum Approach Distance Requirements
Conductor Motion
Laboratory Tests of Prototype Upgraded Structure
14.7 EXAMPLES OF VOLTAGE UPGRADES
Example 1: 115 to 230 kV Voltage Upgrading
Example 2: 230 to 345 kV Voltage Upgrading
Example 3: 300 to 420 kV Voltage Upgrading
Example 4: 230 to 500 kV Voltage Upgrading
Transmission Lines Above 700 kV
15.1 INTRODUCTION
15.2 RESEARCH TO DEVELOP TRANSMISSION SYSTEMS ABOVE 700 KV
Research to Develop 800-kV Systems
Research to Develop Transmission Systems Above 1000 kV
15.3 CASE STUDIES OF TRANSMISSION LINES ABOVE 700 KV
15.4 HYDRO-QUÉBEC 735-KV LINES IN CANADA
System Planning
Electrical Design
Mechanical and Tower Design
Operation and Maintenance
15.5 AMERICAN ELECTRIC POWER SERVICE CORPORATION (AEP) 765-KV SYSTEM IN THE U.S.
System Planning
Electrical Design
15.6 RUSSIAN 750-KV AND 1150-KV LINES
System Planning
Electrical Design
15.7 EDELCA 765-KV LINES IN VENEZUELA
System Planning
Electrical Design
15.8 FURNAS 750-KV LINES IN BRAZIL
System Planning
Electrical Design
15.9 NEW YORK POWER AUTHORITY (NYPA) 765-KV SYSTEM IN THE U.S.
System Planning
Electrical Design
15.10 ESKOM 765-KV LINES IN SOUTH AFRICA
System Planning
Electrical Design
15.11 765-KV TRANSMISSION LINES IN INDIA
System Planning
Electrical Design
15.12 KOREA ELECTRIC POWER CORPORATION (KEPCO) 765-KV SYSTEM IN SOUTH KOREA
System Planning
Electrical Design
15.13 TOKYO ELECTRIC POWER COMPANY (TEPCO) 1000-KV LINES IN JAPAN
System Planning
Electrical Design
Thanks for the toc, it helps me a lot. I have done a search in the university library and we have the 2nd edition.
I will borrow the book and will talk with the librarians for getting help in obtaining the 3rd edition by an international library loan if possible.
The 3rd eddition is much larger than the original one. Also the 3rd edition has a software for several calculations that is worth the efort.
ie
How to calculate the Audible noise for a non-bundled conductor OH line at 66kV L-L