CSA REQUIREMENT FOR NEUTRAL GROUNDING OF GENERATORS
CSA REQUIREMENT FOR NEUTRAL GROUNDING OF GENERATORS
(OP)
DEAR ALL,
IS THERE ANY SPECIFIC CSA REQUIREMENT FOR EARTHING OF GENERATOR NEUTRAL?
FOR EXAMPLE, TYPE OF NEUTRAL DEPENDS UPON SIZE AND VOLTAGE RATING OF GENERATORS ?
IS THERE ANY SPECIFIC CSA REQUIREMENT FOR EARTHING OF GENERATOR NEUTRAL?
FOR EXAMPLE, TYPE OF NEUTRAL DEPENDS UPON SIZE AND VOLTAGE RATING OF GENERATORS ?






RE: CSA REQUIREMENT FOR NEUTRAL GROUNDING OF GENERATORS
From what I've seen 11kV and up are generally neutral transformer grounded. The lower voltage machines have a mix match from individual grounds, to shared neutral resistors across a station ground bus etc.
RE: CSA REQUIREMENT FOR NEUTRAL GROUNDING OF GENERATORS
That covers 120:208V and 120:240V installations. For higher voltage systems the neutral may be floating, (not recommended) zig-zag transformer grounded, solidly grounded or impedance grounded.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: CSA REQUIREMENT FOR NEUTRAL GROUNDING OF GENERATORS