Terminal Lugs

Terminal Lugs

Terminal Lugs

(OP)
Dear All,

Please confirm me for this small confussion. Can I use non-insulated 600V terminal lug to be used for 11kV arrester circuit ? In my opinion Yes, since voltage will effect to insulation material only so for non-insulated doesn't matter.

RE: Terminal Lugs

I disagree.  Air distance is also a form of insulation.  This is even recognized by UL and can be calculated as part of the insulating requirements.

If you take a 600V terminal block and place 11KV on it, you will likely get arc-over.


 

RE: Terminal Lugs

eskim:

Your basic understanding is not wrong, however in the USA many single conductor lugs are UL listed for only 600V. UL (or equivalent) listing is very important in North America. This perhaps is more to avoid liabilities from misapplications, than anything else.

Some manufactures say on their product datasheets that it is UL listed for 600V and 'recommended' up to 35 kV and with due warning that for higher voltage applications it must be used in conjunction with appropriate stress control termination kits/methods, in accordance with manufacturer's recommendation.

If the installation is all overhead using bare conductors, the metal is metal, it has no voltage rating per say.

You should consult the lug mfr. for their recommendations.


 

Rafiq Bulsara
http://www.srengineersct.com

RE: Terminal Lugs

Many larger sized bare metal compression lugs for power conductors are rated for use at up to 35kV.
 

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: Terminal Lugs

It depends on your application of the lug.  During HV testing, a lot of testing is performed with 600V conductors in free air at voltages >22kV using normal 600V connections.

For a permanent installation, you should do the research with vendors.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources