What could cause a 11KV HV cct breaker to indicate UNBALANCE1 on sepam?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Negative sequence/ Unbalance
|
RE: Negative sequence/ Unbalance
Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.
RE: Negative sequence/ Unbalance
A practical example is the single phase high speed automatic reclosure, during the AR pause, when you're functioning with only 2 out of 3 ph energized, negative sequence will appear. There's no problem for OHL or transformers, but it is a very big issue for generators. An oposite rotating field will occur and the generation unit must withstand 100 or 120 Hz instead of 50 or 60 Hz. Depending on I2 magnitude, some units could withstand for 10 seconds before getting burned. That's why you have to reclose the phase or open the other two very quickly, somewhere between 2 seconds.