Grounding of DC for Substation Trip Unit

Grounding of DC for Substation Trip Unit

Grounding of DC for Substation Trip Unit

(OP)
This is a question about how to ground a DC system.

Currently I am looking at two options and I don't know which is the right way (is one right and the other wrong?).

First where the -ve of the DC is tied to the AC ground system.

The second is where the DC system ground is isolated from the AC system ground.

If people could provide me with some pros and cons of each. According to the Canadian electrical code if I isolate the DC ground I have to have a ground detector.

Thanks
 

RE: Grounding of DC for Substation Trip Unit

Operate ungrounded and use a battery charger with a ground detector option. It can be wired out to SCADA or a local alarm panel. That is the lowest cost, most effective design.

When a ground occurs, the charger will alarm but very little current will flow.

There are several good threads on DC system grounding pro's and con's on this site. Try a search.

RE: Grounding of DC for Substation Trip Unit

It may depend a little on the type of dc system.  For dc control power, such as in a substation or switchgear assembly, the dc system is almost always floated to increase reliability, at least in the US and Canada.  

Yes, some type of ground detection is needed, but that is relatively simple to provide.  

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources