Based on NFPA,how door fire rating can be reduced if fire system there

Based on NFPA,how door fire rating can be reduced if fire system there

Based on NFPA,how door fire rating can be reduced if fire system there

(OP)
I have three wooden doors with fire rating of 45min. These doors are for electrical/instrument shop (max. 220V), mechanical shop and equipment storage. These rooms are inside a building located in gas plant. All rooms are for light duty and minor work.
We received a request to change all to be 90min fire resistance while I think this is too much for such building.
As we installed smoke detectors and fire alarm system in the building, dose this justify keeping  these doors with 45min fire rating.
I would appreciate if someone could help to resolve this issue or if I could have the NFPA doc. that support keeping these doors as fire system installed.
 

RE: Based on NFPA,how door fire rating can be reduced if fire system there

Do not think a sprinkler system will let you reduce door rating,

Normaly it is based on the rating of the fire wall, or the use of the room.

Do you know what building code and edition you are under???

"""We received a request to change """

1. who requested it???

2. What code and section did they site for the request???

RE: Based on NFPA,how door fire rating can be reduced if fire system there

There are no allowences for a reduction in door assembly ratings without fire sprinklers.  If you had sprinkler protection there are available reduction allowances in NFPA 101, 2006 40.3.2.4 and 8.7.1.3

"Fire suppression is a failure in prevention"

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources