Inrush reactor inductance
Can anyone help me about how to calculate the inductance value of inrush reactor which is used for inrush currents during medium voltage capacitor switching...
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
RE: Inrush reactor inductance
http
For a single Capacitor Bank
The inrush current depends on the fault level at the point of connection and the capacitor bank power in MVAr.
The closing peak current is given by:
I inrush= Icapacitor x√2 x √(Scc/Q)
Scc: short circuit power of the source in
MVA at the connection point
Q: capacitor power rating in MVAr.
Regards
Marmite
Contact some cap bank manufacturers' application engineer, if you can. Given the parameters they will size it for you.
Also Google for the topic, you will find a few articles, just to give you an idea.
Rafiq Bulsara
http://www.srengineersct.com