Foundation Inspections - Checklist Sheet
Hi all,
I've been tasked with coming up with a company-wide standard checklist sheet for foundation inspections prior to pouring the concrete and was hoping to tap into the vast pool on knowledge available on this site. I have noted down an approximate outline of what I intend to cover.
Any further suggestions/examples would be greatly appreciated...
Inspection Specifics
-Site
-Date/Time
-Weather
-Inspector
-Contact on-site
-Site Risks
Source Information
-Drawings
-Specification
Inspected Elements
-Blinding layer
-Reinforcement spacing/diameter/cover/support chairs/splices/laps/....
-Shoring
-Waterproofing
-Holding Down Bolts
Observations
Verbal Instruction issued on site
RE: Foundation Inspections - Checklist Sheet
What about the soil bearing condition?  Any soft spots?  Hard spots?  Unexpected conditions?  Conformance with design assumptions?
A couple of thoughts...
For "Holding Down Bolts", I would use "Anchor Bolt Placement" and seperate that to at shear walls and non shear walls (wood walls above}, and "Shear Wall Holddowns", type and placement.
Are you intending to verify the bearing capacity of the foundation soil too during the inspection, or is that by others?
Mike McCann
MMC Engineering
Motto:  KISS
Motivation:  Don't ask
What about Augercast Piles - rebar, size of pile, depth, pile layout.
Mike McCann
MMC Engineering
Motto:  KISS
Mike,
The terminology "holding down bolts" probably indicates nineninenine is not in the US, maybe in Oz.
Thanks Guys, some good suggestions here.
Bearing capacity would be verified by the geotechnical engineer.
Hokie - I'm in Oz, but started out in the UK.
999
If you're not careful the form could get very complicated. I would split the inspection into stages.
1. a General Inspection Form which would be signed off after the blinding has been placed. This could include notes on the prior works such as piles, compaction etc and finally the blinding level and condition.
2. A pre-concrete inspection form that includes formwork, rebar, cast-in items etc.
3. A post-concrete inspection which verifies the foundation has been cast correctly.
OK... upsidedown  wink
Mike McCann
MMC Engineering
Motto:  KISS
I like starter bars to be separate from footing reo
Arguing with an engineer is like wrestling with a pig in mud. After a while you realize that they like it
CASE as part of their Risk Management Program publishes a set of Site Visit Cards, which includes a section on Concrete Spread and Wall footings.  If your firm is a member of ACEC the price is very low, and may offer a good starting point for your project.
dewatering, seepage
treatment of rock such as cleaning, leveling, crack filling, dental concrete, slush grouting, pressure grouting
removal of loose material
removal of soft material
placement of subdrains, foundation drains
over excavation and placement of crushed rock
vapor barrier