iam running a gas generator of 1.5MW Duetz engine which indicting Differetial Current from the control panel.what might be the causes and solution to this problem?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Differential Current
RE: Differential Current
RE: Differential Current
If this is a new installation, I would strongly suspect incorrect wiring or phasing of the CTs.
If the unit had been running successfully and no wiring changes were recently made, you have to assume there is a problem in the generator. You should shut down, isolate the generator, and do at least a megger test and polarization index.
RE: Differential Current
Generally it will mean that you have experienced a fault between your differential CT's. 87 is very reliable when you have cases of a line to ground fault in the stator. Look for cable termination kit failures, transformer failures, anything between the CT's.
I would start with a visual, then begin isolating the bus and start megger testing until you find your fault.
RE: Differential Current
Is this an LV or MV machine?
----------------------------------