Quick Response Sprinkler requirement
Quick Response Sprinkler requirement
(OP)
Can someone PLEASE help me out here. I know in the past I've seen a clear ruling in NFPA 13 showing that quick response sprinklers are required for new construction but I can't seem to find it. The only thing I can find is under thermal sensitivity but that states for light hazard. My application is Ordinary Hazard.
Anyone know what I'm referring to? I knew I should have tagged it when I found it the first time! DOH
Anyone know what I'm referring to? I knew I should have tagged it when I found it the first time! DOH





RE: Quick Response Sprinkler requirement
RE: Quick Response Sprinkler requirement
RE: Quick Response Sprinkler requirement
This is for a preaction system if that helps any?
RE: Quick Response Sprinkler requirement
At this point it's a matter of economics and since hydraulically their is no advantage to using the QR sprinklers (can't reduce the remote area) you can save a few bucks a head and using standard response.
RE: Quick Response Sprinkler requirement
Thanks for all the input!