I am using Shoreguard PZH-7 sheet piling for a walkway retaining wall adjacent to a body of water. Can anyone steer me in the right direction or know of appropriate software to calculate the loads on the wall (8 feet high. 4 feet exposed).
I don't want to use tiebacks.
I don't want to use tiebacks.






RE: sheet piling
Bowles - Foundation Analysis and Design
Das - Principles of Foundation Engineering
Day - Foundation Engineering Handbook
You're asking for the loading on the wall. This is a typical soil loading active and passive pressure problem. The only hiccup I see here is whether or not you should apply a live load surcharge due to a small vehicle (golf cart) for emergency purposes.
Das, in particular, has clear examples on this type of problem.
Another resource that might be helpful is the PileBuck design series.
Regards,
![[pipe] pipe](https://www.tipmaster.com/images/pipe.gif)
Qshake
Eng-Tips Forums:Real Solutions for Real Problems Really Quick.
RE: sheet piling
http://w
Download the US Army Corps of Engineers "EM 1110-2-2504 Design of Sheet Pile Walls":
http:/
See the Section beginning on page Page 4-1
Be sure to determine the soil properties for your project since the success of a cantilever wall is entirely dependent on them. Your preliminary estimate is reasonable (8' long sheeting with 4' cantilever projection) - having cantilever sheetpile wall projection equal to embedment was a 1930's rule-of-thumb, for good soil.