I am try to specify current transformers for the protection of a 25MVA hydro generator. Can somebody help me understand what the CT ratings mean? C400? C800? T400?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: CT rating
It's a quick answer, and you probally need to read more about it.
RE: CT rating
Also see attached link:
h
Rafiq Bulsara
http://www.srengineersct.com
RE: CT rating
For high currents, the key to accurate current into the relay is how much secondary voltage the CT can produce before it saturates.
Keep in mind that for multi-ratio CTs, this accuracy rating applies ONLY to the maximum ratio. As you tap down, the accuracy goes down. So a 1200/5 C400 on the 600/5 tap is essentially a C200 accuracy, just as an example.