In a residence, can I use #6thhn, (copper) to feed from a 70a 2pole breaker in the main breaker panel to feed to a small subfed panel, or do I need to use #6thhn. Also, do I have to size the wire for the breaker being fed from, or for the rating of the sub-fed panel (125a)? Thanks!!
designered
designered






RE: ampacity?
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: ampacity?
designered
RE: ampacity?
For sizing conductor's overcurrent protection look up Article 240 and also the ones related to panelboards. (Search for panelboards and switchboards in NEC).
Rafiq Bulsara
http://www.srengineersct.com
RE: ampacity?
What is the length of the cable? Voltage drop could be an issue with long lines (although in this case it sounds like you are ok). Also will this be run in conduit?
------------------------------------------------------------------------