Checking and Testing of Exciter

Checking and Testing of Exciter

Checking and Testing of Exciter

(OP)
Hi,

May I ask your technical advise as to how can I test if my exciter stator coil and exciter rotor is still in good shape? I took the resistance reading from the exciter stator and the reading is only 2.5ohms. I understand from my previous readings that normally the stator coil is around 10-11ohms??? Can this be the verdict?

By the way, during the troubleshooting, I changed the AVR and changed the rotating diodes , do some field flushing on the stator and the rotor of the exciter, but until now I don't have any output from the generator load side. I did some small test putting a 12V in my F+ and F- while the genset and I did get some readings on the load side. This leads me to the conclusion that my main windings are not burned after all.

This is the reason why I put my concentration on the exciter side. Thanks in advance for your support.

RE: Checking and Testing of Exciter

What size set?
Do you have a megger?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Checking and Testing of Exciter

(OP)
Hi Waross,

Yes I have, I measured the resistance of the exciter stator and its only 2.5ohms. I think I need to  check it out with my megger, what could be the minimum allowable resistance?

Thanks,
Chris

RE: Checking and Testing of Exciter

(OP)
Hi Warross and other professionals,

I've managed to check the insulation resistance on the exciter stator field and  exciter rotor windings and the result is 0.12M on the stator and on the exciter rotor is only 0.02M.

The Main field is about 3-4M and I suspect i don't have problem with this.

As I have read from other generator manuals, such as stamford, the minimum insulation resistance should be at least 1M. Do you agree that my exciter stator and rotor has to be rewinded? By the way this generator is at least 25 years already (Caterpillar)

Any comments and suggestion is very much appreciated. Thanks.
 

RE: Checking and Testing of Exciter

Is the generator working or has it failed in service? What size is this set?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Checking and Testing of Exciter

Post the nameplate details of the generator.

Muthu
www.edison.co.in

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources