Motor Energy calculation...
If I have a 7.5 hp 575VAC motor runing all day and I know what the cost of electricity is (12 cents US per KWH) can I roughly estimate my cost by simply multipying the motor power rating (7.5 HP) x (746 W/HP) x (24 h/day) x ($0.12 /KWH) = $16.12/ day operating cost???
U have to know the motor load though, right? cause it may not draw its rated current under normal operations.. is there a % used to guestimate???
RE: Motor Energy calculation...
The load factor can vary widely - from 20% to 110%. I don't think we can be of much help in that area unless we know more about the load.
Hope that helps.
If you want to determine load, you can attempt to measure speed OR current OR [flow rate AND dp...assuming this is driving a pump].
If you obtain a current measurement, it would also help to know the nameplate full load amps and the nameplate rpm.
The ideal situation is obviously to measure electrical power with a coordinated current, voltage, phase-angle measuring device...I'm guessing that's not practical.
It's a wild guess... as dpc mentioned the wide range 20-110% surely might be encountered in the real world.
Assume 1kw input per HP, Demand charge (7.5 KW)($10.00/KW)=
$ 75.00 to start the motor for the monthl. Total electric bill would be the sum of KWH plus the KW Demand Charge.
http://www.tifac.org.in/offer/tlbo/rep/st152.htm