I have a 500kva Tx 660/2300v
The delta primary winding is open cirucit due to a fault.
Could you advise what kind of resistance I would expect between L1, L2, L3 if one of the windings in the delta winding was open circuit?
What would the effect be on the remaining two healthy windings and their resistance.
Many thanks
The delta primary winding is open cirucit due to a fault.
Could you advise what kind of resistance I would expect between L1, L2, L3 if one of the windings in the delta winding was open circuit?
What would the effect be on the remaining two healthy windings and their resistance.
Many thanks






RE: Primary Delta Transformer winding
L1-L3, R=X Ohms
L2-L3, R=X Ohms
L1-L2, R=2X Ohms
Assuming that the fault did not damage the other windings.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Primary Delta Transformer winding
L1-L2 Open
L2-L3 R=X ohms
L1-L3 Open
that's not the question,
but if you have internal fuses on the high side
and the L1 fuse was open
that's what you would see.