COC of Cooling Tower
COC of Cooling Tower
(OP)
I am working out a EIA for a new thermal power plant in India. For the make up water of the cooling tower sea water which would be desalinated and clarified to a tds content of 32,000 ppm will be used.
The common practice of operation of cooling tower indicates a COC (Cycles of Concentration) of 5-6 with non-sea water.
If I use clarified/desalinated sea water somebady is telling me that COC will be limited to 1,5 max. Is this correct?
In this case the volume of make up water will be much more and the water plant design will be affected.
Can somebody help me ?
The common practice of operation of cooling tower indicates a COC (Cycles of Concentration) of 5-6 with non-sea water.
If I use clarified/desalinated sea water somebady is telling me that COC will be limited to 1,5 max. Is this correct?
In this case the volume of make up water will be much more and the water plant design will be affected.
Can somebody help me ?





RE: COC of Cooling Tower
RE: COC of Cooling Tower
Do you know the chemistry of the desalinated and clarified sea water ? At first sight the recommended COC seems a practical approach, although it will evidently be costly on the treating chemicals and make up water (as you say) resulting from the blow down.
RE: COC of Cooling Tower
rmw
RE: COC of Cooling Tower
Refer to the following: Cycles of concentration are based on TDS and chlorides. http://www.eng-tips.com/faqs.cfm?fid=1152. The comments about materials of construction are pertinent also.