battery sizing
battery sizing
(OP)
I am looking for guidance for sizing battery for low profile substation.
What are the worst case scenario I should cosidere for momentary load ? What breakers or circuit switchers shoyuld be operated in case of fault ?
What are the worst case scenario I should cosidere for momentary load ? What breakers or circuit switchers shoyuld be operated in case of fault ?






RE: battery sizing
RE: battery sizing
RE: battery sizing
IEEE 485 is the guide to develop a DC load profile and subsequent battery sizing for lead acid flodded cells.Also after developing your correct load profile, any battery or charger manufacturer will size the battery using a simple excel sheet.Therefore, the challange is to develop the load profile correctly.
Main points are,
1)to indetify all continuous loads
2)to indetify all momentary loads
3)to indetify the worst case contingency in the swgr or substation concerned.