Constant Voltage Transformer unloaded
Constant Voltage Transformer unloaded
(OP)
Hi I am installing a UPS with an external bypass system in the bypass I am looking to install a CVT to maintain a regulated voltage when the UPS is out of service. When the UPS is in service the CVT will be energised but unloaded will this have any detrimental effect to lifetime of the CVT?






RE: Constant Voltage Transformer unloaded
Be sure that the capacitors are situated below the magnetics and that cooling air is free to move through the CVT. Blocking air is the worst you can do to a CVT.
Gunnar Englund