Calculate heating value at flare

Calculate heating value at flare

Calculate heating value at flare

(OP)
Hello Experts,

how to calculate heating value at flare during equipment steam out operation. We have been observing flame-outs at flare during steam-out step in plant shutdown. Lowering the heating value below desired value (300 btu/scf or 12 MJ/m3) is probably cause for the same.

How to calculate heating value when 200,000 lb/hr 150# steam is diverted to Flare during shutdown?
Can we take credit for steam condensation in the system before it reaches the flare?
What is the impact on flare tip exit gas velocity?

please advise.

thanks.  

RE: Calculate heating value at flare

Since steam has 0 BTU/cf heating value, you can take 100,000,000 scfd of steam  times 0 + Xamount gas scfd times 300 BTU/cf, then divide by sum of (100,000,000 + XAmount) to get new BTU/scf

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources