Im trying to spec a 12.47kV load break switch with a 600A fuse, or close to it. Finding the 600A switch is easy but I cant seem to find a 600A fuse/fuse holder. Only 540A but requires 800A holder, what am I missing?

RE: 15kV Fuse

You need to use double barrel fuse holders and two fuses-300A each. Use only factory tested/approved assemblies.


 

Rafiq Bulsara
http://www.srengineersct.com

RE: 15kV Fuse

Padmount?  Pole-mount?  Metal-enclosed?  Air break?  Vacuum?  SF6?  Current-limiting fuse?  Power fuse?
 

RE: 15kV Fuse

(OP)
Its a basic metal enclosed air load break assembly. Current limiting or boric acid type fuse, or others depending on availability.  

RE: 15kV Fuse

A 600E fuse is common for 5kV switches but not 15kV. Typically these are not sized for overload protection, just fault protection, your upstream brealers relays should be set for the OL. Hard for us to help without more info about your system.  

RE: 15kV Fuse

(OP)
The fuse is for fault protection only. This is a primary feed from the utility for an underground 12kV distribution loop. The primary 12kV feed is supplied from the pole and into a 3 section load break assembly. The main section is fused while two secondary sections unfused to feed seperate 12-.6kV substions which are fully protected. Maybe the main fuse is unnessary as technically protection is being handled via cut-out on the pole however I would like there to be some protection there if possible. I dont see why a westinghouse RBA-800 with a 540E rating wouldnt work?


Utility
   |
   |
 Loadbreak/fuse
 |            |
 |            |
Subsation#1  Substaion#2

RE: 15kV Fuse

Are you not satisfied with the utility fuse for fault protection?  Sounds like for that level of load, the utility will already have something other than a fuse cutout on the pole.  You may also have trouble coordinating a 500+ amp fuse with the utility protection.

If the utility has adequate fault protection why not just let them do the job.  Then they are the ones buying those high dollar fuses.  Hopefully you don't blow them often enough for it to be a problem anyway.

Alan

RE: 15kV Fuse

Why not protect each branch separately?  Then you can use a smaller fuse and you will only loose one branch for a fault instead of both.

RE: 15kV Fuse

(OP)
davidbeach, Its a loop system so each branch needs to be able to handel the entire loop full current. The substations have primary fuses of their own.

Now considering removing the requirement for the fuse however I'm not sure of any code requirements for me to protect that conductor once it enters the building..?

RE: 15kV Fuse

Just picked up on the "metal enclosed" part once you said "it enters the building".  Appears we were all thinking outdoor stuff previously.

Sounds from the voltage that you are in the US?  Code may well require protection once it does enter the building.

Don't do the high voltage non utility stuff but other guys here do.

Alan

RE: 15kV Fuse

(OP)
Actually I'm in Canada. Its a 12.47kV system. If at all possible I will intend to keep the fuse in place. Any ideas would be helpful.

RE: 15kV Fuse

Then I expect Bill will offer some input!

Alan

RE: 15kV Fuse

Your options for fuses this size are limited.
What jghrist said. Parallel SM5's are feasible. You can only get the Fault-fiter in S&C switchgear (they don't sell it to other mfg's).

You might also consider vacuum fault interrupter gear such as Eaton MEP.

Alan
----
"It's always fun to do the impossible." - Walt Disney

RE: 15kV Fuse

A 600A fuse at 12.47kV seems rather large.

The protection coordination should be reviewed as you may encounter problems coordinating with the local utilities upstream protection.

Where in Canada are you located?



 

RE: 15kV Fuse

(OP)
I've spoke with the utility and they are willing to install a non-fused 900A switch so coordination is not an issue. Fault protection will rely on our fuse. Would a 540E be more realistic?  

RE: 15kV Fuse

Not much difference in a 540 or 600 amp fuse (60 amps).smile  I guess if that's what it takes then so be it.  I would still look at a three phase interrupter if the budget will stand it, especially if single phasing is an issue.

Alan

RE: 15kV Fuse

(OP)
I guess I suggested the 540E for availability. Some type of vaccume switch would be nice but pricey and complicated. We have sf6 switches for all the substations and I wanted to keep the main fuse simple.

RE: 15kV Fuse

Alan brings up a good point.  If your 12.5-0.6 kV substations have delta primary transformers and are fed by significant lengths of cable, you could have a serious ferroresonance problem when one fuse blows.
 

RE: 15kV Fuse

(OP)
They're wye primary. I guess I may consider going to a relay, Im worried about the cost.

RE: 15kV Fuse

(OP)
Isnt ferroresonance not as big of an issue at 12kV

RE: 15kV Fuse

Not as prevalent as with the higher voltages but still can occur.

Alan

RE: 15kV Fuse

(OP)
well, given they are wye connected and at 12kV I suspect little issues with 1ph protection. Worse case we will install a vcb later.

RE: 15kV Fuse

(OP)
Still havent entirely resolved this issue. Even with double barrel fuses I cannot seem to get a 600A fuse within a 600A switch. I've checked schnider ele and square D with no luck..

RE: 15kV Fuse

Cutler Hammer RBA-800 series are offered in 450, 540 and 720A.

The 540A rating is really 600A (two fuses in parallel) derated by ten percent.


  

RE: 15kV Fuse

(OP)
Right, but isnt the RBA-800 an 800Amp fuse holder? Does that not require a 1200A switch?

RE: 15kV Fuse

You'll probably have to ask your Eaton rep. I can't tell from the literature. It may depend on your NRTL listing requirements.

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

RE: 15kV Fuse

The bus in your switchgear can be manufactured or modified as necessary to accomadate the RBA-800 fuse mounts.

The price of the fuses gets rather expensive.  I have seen eurpean DIN size fuses used frequently due to lower costs.  Using a vacuum breaker with protection relay may not be that much more cost wise compared with a set of RBA-800's, mounting parts and a set of spare fuse links.

Like alehman said, consult with the eaton rep and local regulations and codes first.
  
 

RE: 15kV Fuse

(OP)
yeah, Im going to get a quote for a sf6 switch vs. fuses. I need to find the number for an actual technical sales rep for some suppliers. I can only seem to find local low voltage reps and online (useless) run-around numbers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources