Drainage Pipe Slope Leaving Storm Water Catch Basin -- three proposals
I have a question with regards to design of a gravity overflow of a storm water catch basin.
I'm about to install a gravity overflow from a 500 gallon catch basin which runs down a 140' drainage pipe into another Tank (already existing on a neighboring property) which then gravity feeds eventually to a county trench. I'm constrained by the existing specs of the neighbor's tank so need to design my side of this system so it will work with his. He already put his tank in for me to use so I cannot easily change it. I can do anything I want on my side since I'm still in the design phase.
It's difficult to determine the needed capacity given the various sources that end up in my Catch Basin (all rain runoff and ground water). We're in a rainy Pacific Northwest rural farmland area so the land is relatively flat. My gut tells me 6" pipe will work.
I sketched out three proposed ideas using 6", smooth walled (not corrugated) drainage pipe at various slopes. See the attached jpg's (and one that has everything). There are pros and cons to each of the three. Which of the three do you think is best? Are there any glaring issues I'm not thinking of?
Thanks for your time.
Here's everything in one pdf:
http://fil es.enginee ring.com/g etfile.asp x?folder=a 6407991-4c 41-4a85-a7 41-e1cf687 d0d63& file=Drain ageProposa l6inch.pdf
Here is each page as a jpg:
http://f iles.engin eering.com /getfile.a spx?folder =295d27ca- 6af4-4051- a05c-ce6a0 0cedd07&am p;file=Dra inagePropo sal6inch_C urrent.jpg
http://f iles.engin eering.com /getfile.a spx?folder =76224bd6- dfdf-4332- 9d25-e72b6 6a53e99&am p;file=Dra inagePropo sal6inch_O ption1.jpg
http://f iles.engin eering.com /getfile.a spx?folder =2153534a- 9b2e-4892- 823e-8d4e2 cbe04fa&am p;file=Dra inagePropo sal6inch_O ption2.jpg
http://f iles.engin eering.com /getfile.a spx?folder =cec7b698- 785e-4808- a28b-11757 4e0edfd&am p;file=Dra inagePropo sal6inch_O ption3.jpg
http://fil
http://f
http://f
http://f
http://f
RE: Drainage Pipe Slope Leaving Storm Water Catch Basin -- three proposals
Richard A. Cornelius, P.E.
WWW.amlinereast.com
Since the 40 gallon tank is 3' higher than the top of your tank, your new gravity connection would serve as a conduit for storm flows to backflow if you will back to your property.
This 40 gallon tank, how is storm water fed to it. Is the rim of this tank flush with the ground, so storm water is fed into it overland from the top? In other words where is natural grade with respect to the rim? (This makes a difference on the potential for water to fill the 40 tank to the top)
I would recommend you look into a 'Tideflex' type check valve at the end of your gravity line. It is like a rubber flapper valve, where a higher water level downstream closes it, should the situation arise.
Otherwise I think option 2 or 3 will probably work fine, if this is just an emergency overflow deal for you in the event of pump outage.
It seems to me that you need to either bypass the neighbor's tank or lower it as well as the pipe to the county trench for a gravity system to work properly.
Another option would be to put a backup generator on the existing pump as well as upgrade the pump if the existing downstream system will take additional flow.
You may want to hire an engineering experienced in drainage systems to design a solution.
I would suggest better options to be:
1) install a second pump and emergency power supply so you can always rely on pumping
2) install a larger or additional catch basin / pond to catch the entire storm. Calculate the size you need. It is not that difficult to do. However, it is probably larger than 500 gallons.
3) install dry well to help drain your catch basin
I did think the outfall capacity of his 40 gallon tank might be an issue. An new additional factor I did not realize at the time of my posting is that there is another neighbor feeding into his 40 gallon tank with a 4" pipe. That tank would get fed by this neighbor's 4" gravity pipe and my intended 6" pipe. But, his outflow from that tank is a 7" pipe. That means there would be a total of 10" coming in and 7" going out. Even without factoring in head calcs, I assume 10" going in versus 7" going out doesn't sound good. None of the slopes of these lines is very steep.
I think I better go back to the drawing board and think about your other suggestions like a pond, dry well, standby generator or lowering his 40 gallon tank and installing a bigger outflow from it.
Thanks very much everyone. I really appreciate your helpful suggestions.
This is probably superfluous to the discussion, but the flow rate is correlated to the area, not the diameter.
Of course there are many other factors, but generally the gravity flow capacity of a 7" line is greater than the combined capacity of a 4" and 6" lines provided they have the same hydraulic grade line slope.
I would run a flatter grade 8" instead of a 6" and have the outlet in the 40 gallon at the same invert elevation or slightly above the the outlet elevation of the 6" in the 40 gallon. This will keep the pipe open in freezing situations.
Labor costs would be the same and the pipe costs for 8" is no much more than 6"/
I would agree with a check valve flapper.
Good luck.
I would suggest doing a drainage area study to find out how much water is going into the beginning of the system for a 25 year storm. That Q=Flow is what will set your minimum pipe size and minimum slope.
For your example say the 500 Gallons per hour = 0.02 cfs. A 6" PVC pipe can handle 0.81 cfs at a 1% slope.
Also the 500 gallon catch basin will just have standing water in it up to the level of the outflow pipe. That is gonna get nasty very fast.
CDG, Civil Engineering specializing in Hillside Grading in the Los Angeles area
http://www.CivilDevelopmentGroup.com