Shorting of NGR on over current

Shorting of NGR on over current

Shorting of NGR on over current

(OP)
I am working on a relay upgrade of an existing switchgear. (CA,USA)  The utility comes in at (fused at 80E) 60kV, and feeds the switchgear at 5kV though a 5MVA Y-Y transformer with a NGR on the secondary. The switchgear has 3 breakers feeding the plant load and a 5MVA generator which also has a NGR.

There is a motor operated switch across the transformer secondary NGR which,I believe, closes via a pickup of current at 10 amps through the NGR using an IAC relay (16.5 seconds at 2x).  

I am not sure of the size of the transformer NGR, though the one on the generator is 200 amps.

As near as I can tell the XO CT relay is used to protect the NGR in case of a fault on the cables to the bus or a bus fault.  

The feeders have ground fault protection and trip at 5-10 amp and a short time dial.  The generator is set the same as the relay on the XO of the transformer.   

I am hoping for some comments about this and if someone else has seen it before and if its a good idea.

Attached is a one line and the trip circuit for the main breaker and the 89 close relay.

RE: Shorting of NGR on over current

That's a new one on me.  Perhaps the intent is to protect a 10-sec resistor if the fault is not cleared promptly?   

RE: Shorting of NGR on over current

(OP)
This is a chemical plant, they don't have much in electrical engineering support, I need to decide to keep it the way it is or come up with something else.   

RE: Shorting of NGR on over current

I have seen a similar circuit working the other way around.
When a volt-meter relay across the grounding resistor inferred a fault current above a certain level, a contactor opened to insert more resistance in series with the NGR to limit arcing damage. Alarms were sent also.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources