Performing insulation resistance test on potential transformers

Performing insulation resistance test on potential transformers

Performing insulation resistance test on potential transformers

(OP)
What is the proper voltage to test High-side to ground for an insulation resistance test on a set of 4200-120V potential transformers?  Specifically, a "maintenance" test as this is older used equipment.  I have the NETA MTS table that says for "electrical apparatus" up to 5000V, the MEGGER test voltage should be 2,500VDC minimum.  Does this apply to PT's?  Does the NETA and the ANSI recommended test voltages differ?

Thank you in advance.

RE: Performing insulation resistance test on potential transformers

NETA Maintenance Test Standards specifies the same test voltage for instrument voltage transformers as for any other transformer.  It's Table 10.5 in my version, which is probably out of date.

 

RE: Performing insulation resistance test on potential transformers

The trick with any transformer insulation tests is to ensure that the winding that is part of the test specimen is tested at the correct voltage.  ie: do not do a 5kV megger on a 120V secondary and hope that it survives.

Other techniques such as grounding the non tested winding are also employed to test primary to core + secondary, or secondary to core + primary.

Be aware of what you are actually testing.  In other words, if you are testing the insulation to the core, ensure that one of your test leads is actually on the core.

As with any winding, insulation resistance tests may not test all the portions of a winding (eg: turn to turn, strand to strand).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources