Heating coil contrlols problem

Heating coil contrlols problem

Heating coil contrlols problem

(OP)
I have a heating coil in an air handling unit that is struggling to maintain room set point without over heating the room. If the control valve is only slightly open say 10% the top of the coil is hot and the bottom is cold. Only when the control valve gets to about 40% open does the entire coil heat up and then it is all of a sudden roasting...... it is giving hugh problems...The poor BMS is struggling to maintain the set ponit and the BMS company is blaming the coil... What you think?? Looks like the modulating valve could be over sized too but this has nothing to do with the coil issue mentioned surely.

RE: Heating coil contrlols problem

Coil and control valve sound oversized. With better control on the valve you might be able to gain control of the space. Possible to consider a Pressure Independant valve?

Possible to reduce loop temperature in the system? Lower MWT would have the effect of reducing the 'size' of the heating coil.

RE: Heating coil contrlols problem

(OP)
Chris

I agree with your comments thanks,  but why is the top of the coil hot and the bottom cold when low flow thro the coil? should it not be even thro out..>?

RE: Heating coil contrlols problem


If it is a lot of outside air that is going over the coil then it might not be oversized. Depending on your climate the heat needed might vary a lot between summer and winter.

You could make a circuit with an extra pump running 100% flow over the coil to have even warming under all circumstances, even if the control valve is at 10%. The control valve will regulate the flow going to the coil loop.
 

RE: Heating coil contrlols problem

Check how the coil is currently piped, is the hottest water entering at the top of the coil closest to the entering air stream?  There could be some air entrainment in the coil affecting flow/heat transfer.
It would likely work best if the hottest water entered low on the discharge side of the coil (counter flow).

The pumped coil will work as well assuming the coil is piped and vented properly.

  

RE: Heating coil contrlols problem

Are you sure you have an equal percentage valve which compensates for the characteristics of a hot water application to provide a control that is close to linear. If you have then look to your controls for proper response and settings.

RE: Heating coil contrlols problem

Walkes is on the right track about your coil being mispiped. Counterflow, bottom to top is what you would likely see under normal circumstances.

RE: Heating coil contrlols problem

How is the coil circuited?
 

RE: Heating coil contrlols problem


Be cautious with respect to the RH requirement.

I mean, are these beans "wet" when they come in and will they loose moisture which you have to remove in order to maintain 65% or do the beans absorb moisture which you have to add in the process ?!?

Be sure the building envelope can handle the 65% indoor-RH.
If (points off) the inner walls/construction get below dewpoint condensation will occur.
(Depends of course on what climate you're in)

 

RE: Heating coil contrlols problem


Oops: ignore my post above, it ended up in the wrong topic...

 

RE: Heating coil contrlols problem

Do we know whether this is a hot water, or steam coil? Did I miss it?

RE: Heating coil contrlols problem

It's steam. Has to be if it's hot on top and cold on bottom - pretty classic for these (unless it's HW piped wrong). Probably sized for 100% OA and way too much muscle for part load heating. Are there face and bypass dampers? If so you may be able to monkey with the clamshell positions when at part load. Or use cooler steam... <-(joke that one was)

RE: Heating coil contrlols problem

(OP)
Hi Its actually LPHW at 80 degC and it is piped corectly but the unit is only running at about 30% capacity, it was away over sized even at 100% i'd say.... and yes looks like the heating coil has way too much muscle. To sort out the problem I turned down the flow rate to really really low flow, barley cracking the balancing valve and tested to ensure it could still do mid winter conditions whcih it can....not ideal but problem sorted...thanks for all the help....

RE: Heating coil contrlols problem

Oh ok - good luck. Usually however high temp and lower flow makes stratification worse. If at all possible, you'd be better off minimizing temperature and maximizing flow (if the system permits).

RE: Heating coil contrlols problem

Is it one control valve per coil? Maybe a 1/3 2/3 setup would work better. If you had to turn the circut setter down that much the 1/3 valve would most likely do the day to day work with the 2/3 valve there for the extra capacity if it gets really cold.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources