Maximum Fill Rate for Refinery Storage Tanks

Maximum Fill Rate for Refinery Storage Tanks

Maximum Fill Rate for Refinery Storage Tanks

(OP)
I need to know guidelines for maximum fill rates for spherical and cone roof tanks.  I have guidelines based on tank suction pipesize for floating roof tanks but not for others.  Please advice standards, API sections or other sources that might have this informations. Thanks!

RE: Maximum Fill Rate for Refinery Storage Tanks

API recommended practice 2003 could be helpful

RE: Maximum Fill Rate for Refinery Storage Tanks

jep.....

Evaluate the fill line size and vent size for the tank yourself.

Reasonable liquid velocities for filling is 10-14 ft/second. Tank vents should be as per API-2000

ENG_TIPs is a two way street.... You should not take and never give...

Please tell us what you finally decide and your reasons for your decision.

-MJC

   

RE: Maximum Fill Rate for Refinery Storage Tanks

You also need to understand the tanks vent system and the material you are filling it with.  Then check your environmental permits as your permit may dictate your max fill rate.

RE: Maximum Fill Rate for Refinery Storage Tanks

and when looking at the vent size, also consider non typical ways the tank can be filled.

one common method that is overlooked is via common pump suction lines between tanks.  it is not uncommon to gravity feed from one tank to another.  this might be via 8 inch lines when the fill line is only a 3" line.

going 10 feet per second in a 3" fill line is something like 225 gpm.  but going with 34 feet of head over 100 feet equivalent length in a 8 inch line is 4000 gpm.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources