VFD ramp times effecting current
2

VFD ramp times effecting current

VFD ramp times effecting current

(OP)
Is it true that the faster a VFD is ramped during a start then the more current will be drawn by the motor.  I have heard this and both seen this in the field.  My question now is why?

I'm thinking that for a faster ramp, the faster the VFD changes frequency fast compared to how fast the motor moves up to speed.  This greater difference causes a greater diff in slip while starting and therfore this greater slip causes more current.

If the ramp time is slow the vfd changes frequency slowly compared to how fast the motor is accelerating to match speed and keeps the slip value lower.  This lower slip difference during acceleration causes lower current.

RE: VFD ramp times effecting current

Pretty much dead on. In fact, when you enable the current limiting feature of a VFD, that's essentially what it will do; sacrifice ramp time in order to keep current within the set limit.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: VFD ramp times effecting current

Why - the motor must produce more torque to accelerate quicker and to produce more torque requires more current input.

 

RE: VFD ramp times effecting current

(OP)
Thanks for the response guys!

So is the current more related to the slip being greater during faster ramps, or the motor trying to accelerate quicker and producing more torque?  Or are these two aspects one in the same?

RE: VFD ramp times effecting current

With a vector drive, the slip can be held relatively constant as the motor accelerates, I believe.   

RE: VFD ramp times effecting current

"So is the current more related to the slip being greater during faster ramps, or the motor trying to accelerate quicker and producing more torque?  Or are these two aspects one in the same? "

The two are pretty much two sides of the same coin. If you set the ramp and solve F = ma for F, that is the torque the drive will try to produce.

If you set the slip, that is like setting the torque. If you solve F = ma for acceleration, that is the rate of acceleration that the drive will try to produce.

The difference is that if you can maintain a set torque and accept the rate of acceleration that you get, the drive should not get into an overcurrent trip problem.

If you set acceleration, the drive might need to protect itself with overcurrent trip.

CJC
http://www.vfdriveinfo.com

RE: VFD ramp times effecting current

(OP)
Is it true also that for a given load a larger motor will accelerate the load faster then a smaller motor at a set speed?

I would think so due to the fact that acceleration time is esentially the difference between motor torque and load torque.  If the torque produced by a larger motor is greater over a given speed range then it will accelerate the load faster than a smaller motor.

RE: VFD ramp times effecting current

It is true, a larger motor will accelerate the load faster. However, if the load inertia is small, it is possible that the increased rotor inertia of the larger motor will offset the increased torque.

CJC
http://www.vfdriveinfo.com

RE: VFD ramp times effecting current

pittengineer, you are right in understanding that acceleration torque = motor torque - load torque. The difference is what provides acceleration.

And, CJCPE is right that in order to precisely caclulate the acceleration time then you will need to know the inertia (load torque) of the entire rotating assembly which includes the motor rotor.  

RE: VFD ramp times effecting current

The motor torque and the amount of slip are more or less directly related up to the breakdown torque.

If you are talking about bigger motors with a VFD then yes the bigger motor would likely be able to accelerate the load quicker but it would still depend on the VFD setup. Typically, a VFD is programmed to accelerate the motor with a fixed acceleration.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources