For a GFCI receptacle, under which of the below will it trip:

A.) Hot and neutral are shorted
B.) Neutral and ground are shorted

My understanding of GFCI's, is that it would trip under (B) since some of the current would be going back on the ground and not all back on the neutral. I think under condition (A) it still see a total current of zero and not trip, but the upstream breaker would trip.

RE: GFCI Operation

You are correct.

However, if hot and neutral are shorted, the circuit breaker upstream will trip...

Good on ya,

Goober Dave

RE: GFCI Operation

Doesn't that depend on there being some small amount of load on the neutral circuit so that it has at least a small votlage rise with respect to ground so that current will flow from neutral to ground? If there is no current in the neutral to begin with. then the neutral will be at ground voltage (because they are tied together in the panel). If they are at the same voltage there won;t be any current.

Neil

RE: GFCI Operation

Yes MAGTiger. The load would need to be energized and drawing some current.

Also it should be pointed out that if the neutral and the ground are shorted at the GFI or anywhere else before it the GFI would not notice at all.

Keith Cress
kcress - http://www.flaminsystems.com

RE: GFCI Operation

Neil,
In the past that was correct, but most of the newer GFCI devices have an additional circuit to detect a neutral ground fault even when there is no current flow on the load side of the GFCI.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources